Thread: Wiring Diagram for Bathroom

  1. #1
    DIY Senior Member nelsonba's Avatar
    Join Date
    Sep 2005
    Location
    Minnesota
    Posts
    116

    Default Wiring Diagram for Bathroom

    I would like to run a new bathroom on one 20 amp circuit. The shortest route for cables would follow this order.

    Panel to GFCI outlet (12/2)
    GFCI outlet to 1st wall sconce (12/2)
    1st wall sconce to 2nd wall sconce (12/2)
    2nd wall sconce to vent fan/light combo (12/2)
    vent fan/light combo to dimmer switch for light and regular switch for fan (12/3)

    Is this possible to do?

    If so, can anyone point me to a wiring diagram or tell me how to do it?

    My other option would be to follow this order, which is easier, just requires more cable.

    Panel to GFCI outlet (12/2)
    GFCI outlet to dimmer switch for light and regular switch for fan (12/2)
    dimmer switch for light and regular switch for fan to vent fan/light combo (12/3)
    vent fan/light combo to 1st wall sconce (12/2)
    1st wall sconce to 2nd wall sconce (12/2)

  2. #2

    Default

    First, you need a 20 amp circuit (12=2) from the panel JUST for the outlet.




    Your lighting circuits will be seperate. Here (AZ) we can use 15 amp (14 ga wire) for lighting.


    The standard method would be home run from panel (or 120 feed from closest source) to a 3 gang switch box. (sconces/vent light/vent fan)

    From the 3G sw box, run a 2 wire to the first, and then over to the second sconce.

    Again from the sw box run a 3 wire to the vent/light. Black wire light, red wire vent. (you could also use 2, 2 wires...you will have an extra white)


    If you are switching you sconces WITH your light on the vent/light, substitute 3 gang box with 2 gang box. Run the switch legs as described and tie them together in the switch box.


    I am assuming you are using NM or "Romex".

    Use plastic boxes, don't cut your wire too short and TIGHTEN your wire nuts.

    Avoid running power to the light/vent and dropping the switch leg from there as in your origibal plan. You want as little "make up" as possible in the vent fan or lights.

  3. #3
    Computer Programmer Bill Arden's Avatar
    Join Date
    Sep 2006
    Location
    MN, USA
    Posts
    584

    Default

    1. I would not use 14ga on a 20A circuit even if it is allowed.
    It's this kind of thinking that is the source of the whole Arc-fault issue.

    2. I find that making things logical to be a lot easier to understand latter.
    So use the extra wire and large deep boxes. Check the CU(cubic inch) numbers.

    3. You can not (as I understand it) run more than one power source into a box using separate cables. So it's best to use 12-3 or 14-3

    4. Why can't the bathroom have it's own light circuit?
    It would be annoying (and possibly dangerous) if tripping the GFI caused the light to turn off. My house has the bathroom lights wired on the same circuit as the kitchen lights.

    5. I know this is a bit anal, but I like to have the power source enter from the top of the box and have loads exit out of the bottom. I know it makes "make up" a little more complex, but I also tend to use larger boxes.
    Important note – I don’t know man made laws, just laws of physics
    Disclaimer: I'm a big fan of Darwin awards.

  4. #4
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    976

    Default

    Unless a local amendment prohibits it you most certainly CAN have the receptacle and lighting on the same circuit in a bath. That is provided that circuit does not leave the bathroom. This is common in smaller half-baths and such.

    In a full "main" bathroom I would not do it this way. Not for GFI reasons though. There is NO rule that the lighting must be GFI protected, so a tripping GFI is not an issue. It's more a practical issue. Many hair dryers already use most of a circuit, so adding lights and a fan can overload the circuit tripping the breaker, not the GFI.


    I would also run a dedicated 20A circuit for the receptacle. Then I'd run a new (14/2, 15A) circuit for the lighting, unless you can find a lightly used lighting circuit you can tap off of. If there is room in your panel a dedicated lighting circuit is the way to go.
    I promise you, you do not want to have to make up the fan/light with #12 wire. Especially a Panasonic.

  5. #5

    Default

    1. I would not use 14ga on a 20A circuit even if it is allowed.
    It's this kind of thinking that is the source of the whole Arc-fault issue.
    If you were referring somehow to my post, you must have misunderstood something.



    3. You can not (as I understand it) run more than one power source into a box using separate cables. So it's best to use 12-3 or 14-3

    Sure you can.


    5. I know this is a bit anal, but I like to have the power source enter from the top of the box and have loads exit out of the bottom. I know it makes "make up" a little more complex, but I also tend to use larger boxes
    Not complex but messy. Running everything in the top allows the wires to be folded in more neatly, giving more room for devices. It also allows for them to be removed/relocated more easily ( I do a LOT or rework).

    You can still be anal if you like. Just run the line in the left and the load(s) out the right

  6. #6
    DIY Senior Member nelsonba's Avatar
    Join Date
    Sep 2005
    Location
    Minnesota
    Posts
    116

    Default How about this...

    OK. So I'll wire just the 20 amp circuit to the GFCI outlet with 12/2.

    For the rest, what should I do?

    1) I'll run a separate 15 amp line for the lighting/vent. Do think I'll be able to chain the sconces on to the vent/light combo? It's a Nutone. I'd like to control all the lights with one switch.

    2) There is a bedroom adjacent to the new bathroom. I had to reconfigure some of the walls and now I need to add some outlets. These need to be ARC-Fault correct? Is 15 amp fine?

    3) I'll have a new closet adjacent to the bedroom as well. Can I just tie into the new bedroom outlet circuit for the light?

    4) I'll also have an unfinished storage space and would like to put in a light.

    5) I'll also be adding an outlet to a landing area just outside the bathroom. Can I tap into the bathroom lighting circuit for this?

    6) When running a wire to a switch and then continuing on to anther light or receptacle can I run the power source into the switch box, wire the switch to the wire running to the light, and then pigtail in an outgoing wire that would continue on as a power source to another switch or outlet? If so, is a standard single gang deep box sufficient if it's 14ga wire?

    7) I'll also have an electric heater on it's own 20 amp circuit.

    Can I do the following?

    Circuit #1: 20 amp to bathroom GFCI outlet

    Circuit #2: 20 amp to bathroom heater

    Circuit #3: ARC-Fault 15 amp to bedroom outlets and new closet light

    Circuit #4: 15 amp to storage space light, bathroom lighting, landing outlet.

    I have two open spaces in my breaker box. I'd have to replace an existing 15 amp breaker with a 15 amp cheater, add a 20 amp cheater, and add the 15 amp ARC-Fault Circuit.

    Thanks!

  7. #7

    Default

    Let's get a few items straightened out first.

    1. It is absolutely permissible to have the lights and receps on the same 20a bath circuit. Required bath circuits are covered in 210.11(C)(3)... but there are strings attached.....read & follow the exception. You can put the lights in line before the GFI to keep the GFI tripping from taking out the lights. BUT, once you have something other than the receps on the bath circuit, that circuit cannot leave the bathroom.

    2. It is not permitted to have 14 NM on a 20 amp circuit. Period. At least not in 99.99% of residential applicatons. Ampacity for NM ("romex") starts in 334.80. Putting 14ga on a 20a breaker has nothing to do with arc fault requirements.

    3. You can have as many circuits as you want in a box, as long as box fill (Article 314) is properly applied, as well as 210.4(B).

    To the OP:

    Sounds like your suggestions in your last post are the way to go. Just keep in mind you can't use AFCI breakers on a multi-wire circuit.
    Just my 2¢ worth.

  8. #8

    Default

    OK. So I'll wire just the 20 amp circuit to the GFCI outlet with 12/2.

    Good idea.

    1) I'll run a separate 15 amp line for the lighting/vent. Do think I'll be able to chain the sconces on to the vent/light combo? It's a Nutone. I'd like to control all the lights with one switch.
    Yes but tie them together at the sw box.


    2) There is a bedroom adjacent to the new bathroom. I had to reconfigure some of the walls and now I need to add some outlets. These need to be ARC-Fault correct? Is 15 amp fine?
    Yes


    3) I'll have a new closet adjacent to the bedroom as well. Can I just tie into the new bedroom outlet circuit for the light?
    yes


    4) I'll also have an unfinished storage space and would like to put in a light.

    5) I'll also be adding an outlet to a landing area just outside the bathroom. Can I tap into the bathroom lighting circuit for this?
    Yes, provided you went with the seperate lighting circuit.


    6) When running a wire to a switch and then continuing on to anther light or receptacle can I run the power source into the switch box, wire the switch to the wire running to the light, and then pigtail in an outgoing wire that would continue on as a power source to another switch or outlet? If so, is a standard single gang deep box sufficient if it's 14ga wire?
    Yes but there isn't a standard size. Go with the deepest box you can find (22ci?)



    Can I do the following?

    Circuit #1: 20 amp to bathroom GFCI outlet

    Circuit #2: 20 amp to bathroom heater

    Circuit #3: ARC-Fault 15 amp to bedroom outlets and new closet light

    Circuit #4: 15 amp to storage space light, bathroom lighting, landing outlet.
    Yes


    I have two open spaces in my breaker box. I'd have to replace an existing 15 amp breaker with a 15 amp cheater, add a 20 amp cheater, and add the 15 amp ARC-Fault Circuit.

    The AFCI will need a full space.

    I wouldn't put a heater on a twin breaker.

    I would put all the 15 amp stuff together.

    If you have to relocate wires to make room, make sure none of the wires are red. That's a whole nother issue.

  9. #9
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    Quote Originally Posted by nelsonba View Post
    I have two open spaces in my breaker box. I'd have to replace an existing 15 amp breaker with a 15 amp cheater, add a 20 amp cheater, and add the 15 amp ARC-Fault Circuit.

    Thanks!
    In addition to what Alectrician said... check the inside panel of the breaker box, it should tell you how many circuits it's rated for. There's a limit to how many cheaters you can use.
    Master Plumber Mark:

    there is nothing better than the
    manly smell of WD 40 in the air
    while banging away on brass with a chisel and hammer...

    it smells like......victory......

    do not hit your thumb...
    __________________
    Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.

  10. #10
    DIY Senior Member nelsonba's Avatar
    Join Date
    Sep 2005
    Location
    Minnesota
    Posts
    116

    Default Couple more questions

    Why not put a heater on a twin breaker? The heater draws 1500 watts.

    The boxes I got for the sconces are metal. Do I need to pigtail a ground wire to them?
    Just keep in mind you can't use AFCI breakers on a multi-wire circuit.
    Are you talking about a double breaker? I realize I'll need a full pole just for the AFCI breaker.

    Thanks!

  11. #11

    Default

    I don't feel that the twin breakers handle bigger continuous loads well.



    Plastic boxes are non conductive=safer. You must bond the metal box. Use one of the NM grounds instead of adding a ground pigtail.


    Stay away from red wires in panel....multi wire branch circuits...two hots, one neutral. Hots must be on seperate phases (legs)

Similar Threads

  1. Help with wiring diagram
    By eric3872 in forum Electrical Forum discussion & Blog
    Replies: 8
    Last Post: 02-25-2012, 07:20 PM
  2. Cooper 6105 wiring diagram conflicts
    By nrthwds in forum Electrical Forum discussion & Blog
    Replies: 9
    Last Post: 02-07-2011, 07:10 AM
  3. Wiring diagram for bedroom
    By oxicottin in forum Electrical Forum discussion & Blog
    Replies: 15
    Last Post: 11-01-2010, 05:34 PM
  4. Can someone double check my wiring diagram?
    By dizzo72 in forum Electrical Forum discussion & Blog
    Replies: 5
    Last Post: 04-11-2010, 11:14 AM
  5. Basement bathroom rough in diagram feedback?
    By gerryuml in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 18
    Last Post: 04-04-2009, 06:25 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •