    Default single pole double circuit breaker

    Are these legal under NEC?

  2. #2
    DIY Senior Member BrianJohn's Avatar
    Join Date
    Jun 2007
    Location
    VA
    Posts
    151

    Default

    Does it have a UL or equivalent seal/sticker, if so yes.

  3. #3
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    It appears that you are talking about what is often called a "Tandem" breaker that connects to one side of the load center, and contains two separate circuit breaker devices with two handles.

    The only risk would be if someone incorrectly connected both hot wires of what was intended to be a multiwire branch circuit, with only one neutral, to both terminals of a tandem breaker.

  4. #4
    DIY Junior Member Igor's Avatar
    Join Date
    Dec 2007
    Location
    Oregon
    Posts
    19

    Default

    See http://www.ul.com/regulators/novdec2002.pdf for UL's position on the use of tandem breakers.

    The 42-circuit limit, which dates back to the 1930's when flammable rubber-insulated wire was used, is going to be removed in the 2008 edition of the NEC.