(206) 949-5683, Top Rated Plumber, Seattle
Results 1 to 13 of 13

Thread: Failed GFCI?

  1. #1
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default Failed GFCI?

    While working around a receptacle outlet yesterday, I was rewarded with a loud POP when a hot terminal brushed the (steel) box. The screw head was slightly vaporized, with a matching pockmark in the box. The main 20A breaker tripped. Problem is, this was a downstream receptacle from an upstream GFCI, and the GFCI did not trip. I reset the main breaker, pressed the GFCI's TEST button, it tripped, and both it and its downstream receptacles went dead. It's a 2-month-old P&S GFCI made in (gulp!) China. The wiring all checks OK, and a 3-light tester shows all receptacles wired properly.

    If I had been naked, standing in a bathtub full of water, and grabbed that receptacle hot side, I'd probably be dead. Is there any other explanation of what went wrong other than a failed GFCI? If it's bad, why does it test OK? These things are supposed to trip at 6ma within 25ms. I'm going to make up a GFCI tester I can plug in to test downstream receptacles individually and will post the results.

  2. #2
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    You can purchase a GFCI tester that will tell you if the GFCI is within specs. when it trips.

    I would recomend buying one of them instead of making one your self.

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    There were a lot of GFCI recalled earlier this year. Probably chinese. Problem was they didn't trip. I will try to find the recall info. What brand are yours?

    This recall is from 2003, but I think the same brand was in trouble eariler this year.>>
    http://dbs.idaho.gov/electrical/Notices/gfci.pdf
    Last edited by jimbo; 11-15-2007 at 04:38 AM.

  4. #4
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    Jimbo it is a P&S

  5. #5
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    Quote Originally Posted by Cass View Post
    I would recomend buying one of them instead of making one your self.
    Yeah, but then I'd have to get out of my jammies and go shopping . Guess I'll have to bite that bullet. I've e-mailed P&S tech support for advice also.

  6. #6
    Electrical Contractor sbrn33's Avatar
    Join Date
    Jul 2007
    Location
    Fremont, NE
    Posts
    31

    Default

    The GFCI is probably alright. What you had was a short to ground and the breaker did it's job quicker than the GFCI. If you had been standing in water and touched the hot wire and ground the difference in potential would have made the GFCI trip.

  7. #7
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    Do you know that the downstream circuit was connected to the protected load terminals of the GFCI breaker?

    You get two choices when connecting a GFCI and one choice doesn't protect the downstream circuits.

  8. #8

    Default

    Quote Originally Posted by Mikey View Post
    Yeah, but then I'd have to get out of my jammies and go shopping .
    Why get dressed?

    GFCI tester
    Last edited by 480sparky; 11-15-2007 at 09:37 AM.
    Just my 2 worth.

  9. #9
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default You learn something new every day

    sbrn33 -- you got it mostly right. Here's P&S's response:

    If the steel box was properly grounded, then yes, this definitely would have caused a differential current in the GFCI (very high current in the line leg, no return current in the neutral). If this was the case, then very simply, we think the circuit breaker just tripped out sooner than the GFCI did. A typical trip time for a magnetic circuit breaker with this type of overcurrent is 10ms or less. Our GFCI response is about 25ms.

    Sounds like everything worked exactly as it should.

    The GFCI's you have, based upon the tests you performed, are working properly.

    Mike Gaines, Technical Support
    Pass & Seymour/legrand

    Bob -- yes, everything is connected properly.

    Sparky -- I think they put you in jail for that in this county.
    Last edited by Mikey; 11-15-2007 at 09:10 AM. Reason: added title

  10. #10

    Default

    Quote Originally Posted by Mikey View Post
    Sparky -- I think they put you in jail for that in this county.
    For what? Buying from fleabay?
    Just my 2 worth.

  11. #11
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default

    No, going to Lowe's in your jammies.

  12. #12

    Default

    Quote Originally Posted by Mikey View Post
    No, going to Lowe's in your jammies.
    The link is for a GFI tester listed on Fleabay.
    Just my 2 worth.

  13. #13
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,685

    Default Oh, THAT's what it was

    The link got trashed by the forum censor... I'll look there, though. There appear to be cheap testers and expensive testers. I assume the cheap ones just generate a 6ma load and see if things trip, whereas the expensive ones will tell you how long it took to trip as well? I made a half-*ssed attempt to find an internal diagram of a GFCI, but all of the images I found weren't available for one reason or another.

    Found the Triplett Plug Bug on that site. They're cheaper at my local Lowe's (GB, not Triplett, but one of the "cheap kind" of testers).

    There's a Greenlee 5708 there, which is expensive ($90) but I don't see why it's any better than the $7 ones. It's apparently the base device for a bunch of test sensors, but even the Greenlee Web site is pretty sparse in its description of the thing.
    Last edited by Mikey; 11-15-2007 at 05:30 PM. Reason: Added 2nd & 3rd paras