I curently have a 3 zone system. 1 zone is for an indirect hot water heater and the other 2 are heating zones. I would like to create 2 more zones. The zone valves are honeywells. They are 24volt vales and my system has 1, 24 vold transformer. I was wondering home many valvas I can run off that transformer? Is there a limit? I want to avoid adding to the exixting loops as to not create a long run.

Thanks,
Chris
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
the spec sheet for the valves will have a VA or wattage. Add them up, and compare with the available current for the transformer...you might be okay, but you may need a bigger one.
 

Steven62

New Member
Messages
9
Reaction score
0
Points
0
Location
Missouri
adding zone

If you still need help with this, give the guys at Watts Radiant a call. Ask for Hydronic technical help. 800-276-2419
They will help you design the best option!
 

Rockycmt

Member
Messages
166
Reaction score
1
Points
18
Location
New York Metro Area
Thanks for that contact. I will try it.

Also,
Out of my boiler I have threaded iron pipe(I guess). Can I convert it to 1 inch copper to add 2 zones. I am very familiar with sweating copper and rather do that then rent a threader to build off the current manifold.
 