Thread: light in shower

Hybrid View

  1. #1
    DIY Member gfe76's Avatar
    Join Date
    Dec 2004
    Location
    Florida
    Posts
    88

    Default light in shower

    Roughing in standing shower. thinking about putting a shower ceiling light in with switch right outside shower threshold. Anything special about putting a light in ceiling of shower? (I plan on having a 16" square access panel in shower ceiling to get accesss to shut off valves.)
    Thanks

  2. #2
    Aspiring Old Fart, EE, computer & networking geek Mikey's Avatar
    Join Date
    Nov 2005
    Location
    Central Florida
    Posts
    2,504

    Default

    2005 NEC 410.4(D) says your lighting fixture must be listed for the location. I would also put it on a GFCI-protected circuit, assuming the switch is close by.

  3. #3
    DIY Member gfe76's Avatar
    Join Date
    Dec 2004
    Location
    Florida
    Posts
    88

    Default

    thanks mikey...that's what I thought (although I didn't know the code section). Can these lights be purchased at big box store as long as it says suitable for showers (wet conditions)? thanks

  4. #4
    DIY Senior Member rdtompki's Avatar
    Join Date
    Dec 2005
    Location
    Iowa
    Posts
    115

    Default

    Whe you say "light" I assume you mean a recessed fixture. You just need to make sure that the fixture has a trim option that is approved for damp conditions. I believe most do. There is certainly a limitation as to how close you can place an outlet to a tub. I don't know that this applies to switches and showers, but I wouldn't necessarily put the switch within arms reach of the shower.

    Rick
    Last edited by rdtompki; 11-06-2007 at 11:22 AM. Reason: correction

  5. #5
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    922

    Default


  6. #6
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    922

    Default

    Also, no GFI protection is required for recessed lights over a tub or shower.
    You can if you want, but it is NOT required.