This is my first post in the electrical forum. I am remodeling my master bath and want to add scone lights next to mirrors. I am a DIYer but very limited with electrical work, but I can follow instructions.
To no big surprise I cant get anyone to do a small job like this.:(

Anyway attached is a .JPEG image of what I am trying to do:
1. the wall is open and I have good access to the work
2. I want to tie in a switch to existing outlet
3. run romex to 4 light scones swtich approx 4-9ft. away.
4. add boxes to each
concerns:
The wall outlet is not GFCI(no test switch etc.)
My wife uses this outlet for a high wattage hair dryer -chance this would trip the breaker?

Any input/suggestions?
thanks
 

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
1. the wall is open and I have good access to the work
2. I want to tie in a switch to existing outlet
3. run romex to 4 light scones swtich approx 4-9ft. away.
4. add boxes to each
concerns:
The wall outlet is not GFCI(no test switch etc.)
My wife uses this outlet for a high wattage hair dryer -chance this would trip the breaker?

Regarding #1: All the better!
#2, is this existing outlet on a dedicated 20a bath circuit? If not, I'd suggest installing one.
#3: The 20a bath circuit can feed the lights, but if you do, the circuit cannot feed anything outside the bathroom. If the existing circuit is not a dedicated 20a bath circuit, you can you it instead.
#4: Required.
GFCI: All receptacles in the bathroom must be protected. If you have more than one, you can 'line-load' one GFCI receptacle to protect another.
Hair dryer: Should be fine on a dedicated 20a bath circuit. Hair dryers are the reason the circuits are required.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
circuit

If the dryer blows the circuit you need a bigger circuit. If the lights are on the same circuit as the outlet and the dryer blows the circuit, the lights will go off also.
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
Depending on the age of the house and the builder, the outlet may be a feed-through from a gfci placed elsewhere. WHile not the best idea, that's how mine was wired...as an extension from a half-bath below. Best to dedicate a circuit to it if possible.

Unswitched outlets are preferable, to me at least, in the bathroom. So, I'd look to change that outlet to a gfci.

Depending on the size of the box and where power is coming from, you may need to replace the box if you are going to use it as a junction...there is a limit on how many wires you can run through a box.

Since things are open, it's fairly easy to add new wires. As noted, you may want to run a new circuit from the power panel.

A picture would help, and then maybe a diagram of how it is currently wired would make it clearer.

There is an anti-spam feature that requires a few posts before you can post pictures. Didn't notice how many posts you have, but I think it is 3.
 

Chris Fox

Member
Messages
158
Reaction score
0
Points
16
Location
near Phoenix AZ
Sorry guys...
Heres a existing and proposed.
I decided to change this a bit, since I have 2 outlets - each end of the long sink I would like to split up the 4 scone lights(his/her controls for each sink).

Thanks for all the replies, this is probably my biggest challenge for this master bath project.

chris
 

Attachments

  • lighting_existing.jpg
    lighting_existing.jpg
    29.1 KB · Views: 392
  • lighting proposed.jpg
    lighting proposed.jpg
    37.6 KB · Views: 403

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
If I'm looking at this right, you have a circuit that enters the bathroom, goes to two receptacles, and then exits the bathroom. Correct?

If so, you cannot use this circuit for what you want to do. You can certainly use it for the lights, but not for the receptacles.

Code reference is 2005 NEC 210.11(C)(3):



I would suggest using the existing circuit to supply the lights, and install a dedicated 20a circuit for the two receptacles.
 
Last edited by a moderator:

Chris Fox

Member
Messages
158
Reaction score
0
Points
16
Location
near Phoenix AZ
I uploaded the pics without reading some of the replies.
The outlets are protected somewhere in the line but not at the actual switch. I can change these out.
The romex trail(drawin in the illustration) goes on to another part of the house(in line).
I was looking into adding another switch to light switch bank for the bathroom but it is on a opposing wall. I dont want to tie into the existing lights(recessed ceiling). This is my backup plan if my proposed design dosent work.

Hope this helps..
Chris
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
If I'm looking at this right, you have a circuit that enters the bathroom, goes to two receptacles, and then exits the bathroom. Correct?

If so, you cannot use this circuit for what you want to do. You can certainly use it for the lights, but not for the receptacles.

Code reference is 2005 NEC 210.11(C)(3):



I would suggest using the existing circuit to supply the lights, and install a dedicated 20a circuit for the two receptacles.


The recepticals are existing...why is it he can no longer use them??
 
Last edited by a moderator:

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
The recepticals are existing...why is it he can no longer use them??

"Such circuits shall have no other outlets."

Since the circuit leaves the room, it goes somewhere else. So it has other outlets.

If you want to 'grandfather' this installation, you probably have a case. But as long as the walls are opened up, now is the time to make sure there's enough power for the hair dryer. After all, it's "Home Improvement", not "Home Improvise".
 

Chris Fox

Member
Messages
158
Reaction score
0
Points
16
Location
near Phoenix AZ
ok, plan B...

Heres my alternative:
Work off the existing line for lighting. Its on the opposing wall but can fish romex through.
Proposed idea 1.:
Add another switch to the bank of 3(recessed, shower and tub light,fan)
Any issues of a 4th line(again electrically challenged:D)?
Proposed idea 2.:
add a section of romex off the 3rd recessed light.

Proposed idea 2 is pretty basic, but 7 lights of one circuit seems a little much.

Is it a prey basic job to do idea 1??

thansk again for the quick feedback I have been getting...
Chris
 

Attachments

  • another approach.jpg
    another approach.jpg
    34 KB · Views: 394
  • propsoed idea 1.jpg
    propsoed idea 1.jpg
    46.8 KB · Views: 379
  • propsoed idea 2.jpg
    propsoed idea 2.jpg
    49.7 KB · Views: 390

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
Any of those proposals would be OK. How many lights and switches you have is strictly a design choice.
 

Chris Fox

Member
Messages
158
Reaction score
0
Points
16
Location
near Phoenix AZ
Sparky,

What would you recommend in this case? Design wise.
If I go with 1, having its own switch, is it pretty straight forward for adding another switch to this existing source(I guess its easy as copying the other 3 switches)
thanks
 

480sparky

In the Trades
Messages
149
Reaction score
0
Points
0
How many switches and lights you have is a personal choice and one I won't get into.

My only suggestion at this point is to install a 20a dedicated circuit for the receptacles. Install a GFI at the first one, and you can protect the other one from there. That way, if the hair dryer does trip the breaker, she's not standing there in the dark. Just remember these two:
.............................................
 