    Is there any reason why I can't have my new water heater installed as per the picture attached? Where the dryer currently is.
    Attached Images Attached Images  

  2. #2
    In the Trades Bob NH's Avatar
    Join Date
    Oct 2005
    Location
    New Hampshire
    Posts
    3,307

    Default

    It appears that you have two fired units going into one flue. That is usually an unacceptble situation, whether the heater is where it is or where you want to put it.

  3. #3
    Plumber patrick88's Avatar
    Join Date
    Sep 2007
    Location
    Webster Ma.
    Posts
    836

    Default

    It looks like that will be ok.
    I'm just starting to work with an old friend of mine to bring solar electric and hot water systems, wind turbines, Flex Fuel Boilers, batteries, hydroponic gardening, books, pellet grills and more. Also the parts for DIY installation.

  4. #4

    Default

    I sure hope it is acceptable as the new flue liner is only 18 months old? It was a reputable company that installed all of the new venting. Didn't need a water heater at the time.

  5. #5
    Plumber patrick88's Avatar
    Join Date
    Sep 2007
    Location
    Webster Ma.
    Posts
    836

    Default

    If you posted the state/city/town etc... you live in it would be a lot simpler to tell you what is in code for you.
    I'm just starting to work with an old friend of mine to bring solar electric and hot water systems, wind turbines, Flex Fuel Boilers, batteries, hydroponic gardening, books, pellet grills and more. Also the parts for DIY installation.

  6. #6
    General Contractor Carpenter toolaholic's Avatar
    Join Date
    Jul 2005
    Location
    Marin Co. Ca.
    Posts
    829

    Thumbs up See Folks

    THIS IS WHAT I WAS TALKING ABOUT !!!!! Thank's Pat

  7. #7

    Default

    Quote Originally Posted by Bob NH View Post
    It appears that you have two fired units going into one flue. That is usually an unacceptble situation, whether the heater is where it is or where you want to put it.
    I'm not so sure about this..... It is done all over the place (and legal) in the Northeast. A rough calculation is that the flue is sized for the largest diameter gas fired flue + 50% of the second size. For the acutal calculation you can reference one of the B-Vent companies product specifications (you need to know the BTU of each appliance). www.hartandcooley.com or www.mtlfab.com

    Check with your township, state, but here as long as your using the right size for total BTU you would be allowed to combine them.
    Last edited by dowop; 10-23-2007 at 06:43 AM.

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default heater

    The only time it would not work is if either of the units had a powered flue. Then the forced draft one would backdraft into the other one.

  9. #9
    General Contractor Carpenter toolaholic's Avatar
    Join Date
    Jul 2005
    Location
    Marin Co. Ca.
    Posts
    829

    Talking

    In N. Ca. ,older homes have this same set up all over , no problem.

    This is a prime example why D I Y should list their state and city.
    We promise not to tell any x wives out there,REALLY