Page 2 of 2 FirstFirst 12
Results 16 to 21 of 21
Thread: subpanel ground rod location and installation
  1. #16
    scratch-pad engineer and mechanical fabricator leejosepho's Avatar
    Nov 2006
    Overall then, and I am probably not going to like the answer here, I will have to run conduit? Coming off a 60-amp breaker, I will be going just a little under 50' to the subpanel, and I am assuming I cannot run a bare ground wire between floor joists and through walls alongside a 3-strand "Romex" of the proper size ...
  2. #17
    Jun 2007
    North Carolina
    300.3(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
  3. #18
    Jun 2007
    NY State, USA
    Define "3 strand romex". Do you mean "3-wire"? As in black, red, white, ground?
    If it is 3-wire then the ground will be the proper size automatically.
    If it is 2-wire then it was never correct in the first place.
    Now I'm confused....
  4. #19
    Nov 2006
    Quote Originally Posted by Speedy Petey View Post
    I have in the past worked with 4-wire SJ cord wiring 3-phase motors and such, but I do not recall ever seeing 4-wire "romex". So, I was mistakingly thinking about black-white-ground 3-wire cable while assuming I would have to add a ground wire to get a total of four ... and I now realize all of that would incorrectly add up to 2 hots and two grounds.
  5. #20
    Jun 2007
    NY State, USA
    Quote Originally Posted by leejosepho View Post
    Exaaaaactly.
    You need ... hot, hot, neutral, ground ...in the same cable or raceway.
  6. #21
    NM cable for example, 6-3wG, or 4-3wG is four wire cable.