    Overall then, and I am probably not going to like the answer here, I will have to run conduit? Coming off a 60-amp breaker, I will be going just a little under 50' to the subpanel, and I am assuming I cannot run a bare ground wire between floor joists and through walls alongside a 3-strand "Romex" of the proper size ...

  2. #17
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    300.3(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).

  3. #18
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Define "3 strand romex". Do you mean "3-wire"? As in black, red, white, ground?

    If it is 3-wire then the ground will be the proper size automatically.
    If it is 2-wire then it was never correct in the first place.

    Now I'm confused....

  4. #19
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by Speedy Petey View Post
    Define "3 strand romex". Do you mean "3-wire"? As in black, red, white, ground?

    If it is 3-wire then the ground will be the proper size automatically.
    If it is 2-wire then it was never correct in the first place.

    Now I'm confused....
    I have in the past worked with 4-wire SJ cord wiring 3-phase motors and such, but I do not recall ever seeing 4-wire "romex". So, I was mistakingly thinking about black-white-ground 3-wire cable while assuming I would have to add a ground wire to get a total of four ... and I now realize all of that would incorrectly add up to 2 hots and two grounds.

  5. #20
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by leejosepho View Post
    and I now realize all of that would incorrectly add up to 2 hots and two grounds.
    Exaaaaactly.
    You need ... hot, hot, neutral, ground ...in the same cable or raceway.

  6. #21

    Default

    NM cable for example, 6-3wG, or 4-3wG is four wire cable.