1) If the floor drain is adequately vented, there shouold be no need for any additional vents (beyond the other floors that is)Originally Posted by dondiy
2)External cleanout should be good enough - include cleanouts in each fixture group as well - if there is a problem later you will be glad you did
3)Yes you can use air - only use 5PSI though...
We generally use a 10' head of water for underground testing (and above ground if there is no drywall up yet...)