I am going to change my panel from fuses to breakers.
What is the easiest way to kill main power to the fuse box ?
 

Jbfan74

Electrical Contractor
Messages
135
Reaction score
1
Points
18
Location
Newnan, GA
Have the power company disconnect it for you. You may have to upgrade your incoming wires also.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
DarylF08 said:
I am going to change my panel from fuses to breakers.

WHY?????????

As an engineer you should already know that fuses are a lot safer than breakers
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Pull the meter and disconnect the load side swinging the old meter out of the way.

Install new service and then jump from the load side of the old meter to the new service and call for inspection.

Here is a picture of an underground service that is being changed for the installation of a generator. It will give you an idea of how to use the old meter to maintain power to your house while you wait on the inspection department and the power company.

GeneratorPictures10-18-06004.jpg
 
Last edited by a moderator:

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
DarylF08 said:
City Code now requires me to upgrade to a 100amp service with breakers.
How can the "City Code" require an upgrade????
Do you mean "require" as in mandatory???
 

Statjunk

DIY Senior Member
Messages
540
Reaction score
0
Points
0
The last home I purchased the insurance companies would not insure me unless I had breakers. Silly isn't it. They actually wrote me under Michigan Basic until I upgraded the panel.

Tom
 

DarylF08

Mec. Elect. Engineer
Messages
19
Reaction score
0
Points
0
Location
St. Louis Missouri
Speedy Petey said:
How can the "City Code" require an upgrade????
Do you mean "require" as in mandatory???


YES, In order to get a new occupancy permit (selling the property)
You are required to upgrade all 60 amp service to a 100 amp service
with breakers
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,771
Reaction score
1,191
Points
113
Location
New England
It's a lot more likely someone will put in a 30A fuse where a 15 or 20A one was than someone replacing a breaker with the wrong one. There are still some pennies making the connection, too. In today's society, 60A doesn't cut it either...
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
As an engineer you should already know that fuses are a lot safer than breakers


As an electrician you should know that generally a fuse installation is a lot more dangerous than breakers.

There is more to it than the protection factor of the fuse VS the circuit breaker.:cool:

spelling edit
 
Last edited:

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Alectrician said:
As an electrician you should know that generally a fuse installation is a lot more dangerous than breakers.

There is more to it than the protection factor of the fuse VS the circuit breaker.:cool:

spelling edit
Would you explain your thoughts a little?
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
Would you explain your thoughts a little?

I'd be happy to.

Although the fuse itself is apparently does better job of breaking the circuit in an overload situation (I am taking your word for this btw) the entire system is going to be at least 40 years old and is more than likely to have been monkeyed with throughout the years.

When you replace the fuse box you will also be correcting a lot of issues like bonding, repairing brittle insulation and correctly sizing protective devices.

Make my day and agree with me.:eek:
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
fuse

As an engineer you should already know that fuses are a lot safer than breakers

And as an engineer, he also probably knows that fuses, other than Fusetrons, are interchangable, so a 30 amp will replace a 15 amp, and that would not be "a lot safer than a breaker". A Model T Ford may be safer than a Ferrari, because it goes a lot slower, but would you want to go back to it?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Alectrician said:
When you replace the fuse box you will also be correcting a lot of issues like bonding, repairing brittle insulation and correctly sizing protective devices.

Make my day and agree with me.:eek:
Over the years I have saw many service change outs and the panel and riser was all that was touched. There is always been a big misconception that breakers are safer than fuses. This is far from the truth.

As far as the repairing of other defective parts of the electrical system, anyone who surfs these electrical sites will attest to the fact that every day someone will post the question, “can the inspector make me do this when all I am doing is changing the service?â€

These questions alone is enough to lead me to believe that there are a lot of electricians through out America selling nothing more than the cosmetic breaker calling it a safer system.

hj said:
And as an engineer, he also probably knows that fuses, other than Fusetrons, are interchangable, so a 30 amp will replace a 15 amp, and that would not be "a lot safer than a breaker".
I will agree that it is easier to change a fuse to a larger size than to change a breaker to a larger size but with the same breath I must also say that I have witnessed just as many oversized breakers as I have fuses.

The truth of the matter is that a 30 amp fuse will open faster under a fault condition than a 15 amp breaker. I have in the lab at school loaded 15 amp breakers to as high as 70 amps for a period of more than three minutes. A 30 amp fuse will blow at 35 amps in less than a minute.

hj said:
A Model T Ford may be safer than a Ferrari, because it goes a lot slower, but would you want to go back to it?
I will agree that the Model “T†is a lot slower than a Ferrari but the Model “T†is far from being as safe.
 

joe in queens

New Member
Messages
35
Reaction score
0
Points
0
You'll likely have to pull the meter to de-engergize the panel. If your meter has a locking ring, the utility usually needs to come out for an unlock. Around here though, if you wait for the utility you'll end-up watching the seasons change, so usually they're grinded them off (I am NOT suggesting you do this) and the job proceeds.

Problem is, you'll likely have to upgrade the meter pan too or your meter will end-up being a main "fuse". You may also need to upgrade your feeders as mentioned, but the POCO's seem to play fast and loose with feeder sizing, so you may be able to get by with undersized (and perhaps grossely underdized) feeders. Can't tell you how many times I see things like 3/0 for 200A spliced into #2 aluminum and other nonsense like that.

JW, aren't UG services fun? Nice ATS and meter pan set-up. Seems like there's not gap behind, did you cut out the siding to get them mounted so nice and flush? Do you have the rest of the genny install pics?
 

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
DarylF08 said:
I am going to change my panel from fuses to breakers.
What is the easiest way to kill main power to the fuse box ?
I installed a new 200 Amp QO panel to replace an old 100 Amp QO a few months ago. It went easily and quickly with the following process.

1. Called the power company and got a number assigned.
2. Got a permit from the electrical inspector.
3. Installed the new panel adjacent to the old panel.
4. Ran temporary lines from the old panel using lugs on the load side of the original panel. You can do that safely by disconnecting the main. The temporary lines were protected by the main on the old panel.
5. Connected all of the branch circuits to the new panel through the breakers in the new panel.
6. Preassembled the new meter pan, conduit, and weatherhead, and ran the wires from meter pan through weatherhead. I now had an assembly that I could fasten into place in one piece.
7. Installed new (larger) Grounding Electrode Conductor.
8. Installed PVC conduit inside to go from the new panel to the point where the back of the new meter pan would be installed. You could also use SE cable.
9. Called the electric company and the inspector and scheduled the change-over. They told me since I had a service number I could disconnect the service without waiting.

I didn't have to work anything hot. Only briefly without power during changeover from one panel to the other.

On the morning of the service changeover, started at 7 AM:
1. Cut the aluminum service wires on my side of the weatherhead service splice with a pair of Fiskar insulated pruning loppers, and bent them out of the way. The loppers worked great.
2. Removed meter and old service equipment.
3. Installed the new meter pan, conduit and weatherhead assembly with 4/0 aluminum conductors.
4. Ran 4/0 aluminum from the meter pan to the new panel.
5. Called inspector for inspection. About 9 AM
6. Waited for inspector. (about 3 hours)
7. POCO hooked up the power about 30 minutes after the inspector called.
 