The NEC (National Electrical Code) requires one rod for if the tested reading for this one rod is below 25 ohms, they require a second rod a minimum seperation of 6 feet.
Drive two 8 foot rods, the best installation would have a minimum of 16 feet between them, twice the length of a single rod.
Are you planning on installing a lightning protection system, if so the LPS will have testing involved and minimum rods determined by this testing.
Lastly where in the Mountain State?