Well.. Now that we are going on our 4th day without power due to a recent storm, I'm thinking I should put in a generator transfer switch.

Any particular brands recommended? I tend to like square d, but I don't know if they make one.

Thanks,
Steve
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
Often the generator manufacturer will offer a transfer switch package. Check with them first.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
switch

First you need the generator, so you can determine how many appliances can be fed by the transfer switch. Then you buy the correct one, get an electrical permit, and have it installed.
 

Seaneys

New Member
Messages
192
Reaction score
0
Points
0
Location
Chicago Suburbs
hj said:
First you need the generator, so you can determine how many appliances can be fed by the transfer switch. Then you buy the correct one, get an electrical permit, and have it installed.

Yeah.. The problem was I had to scramble to buy the generator when it was obvious the power was going to be down for a while. Something about 600,000 ppl w/o power last week raised my concern.

Steve
 

Furd

Engineer
Messages
448
Reaction score
1
Points
16
Location
Wet side of Washington State
I found a surplus Square D 60 amp, 3 pole switch on line. With the shipping it was about $70. Not too bad for a switch that normally sells for over $400.

I installed this with a separate load center circuit breaker panel that I moved my critical loads to from the main panel. Since I had previously installed the load center (I didn't have enough circuit breaker space in the main panel) it was a fairly inexpensive job.
 

Furd

Engineer
Messages
448
Reaction score
1
Points
16
Location
Wet side of Washington State
Three-pole, double-throw, center off with positive stop in the center position.

P1000416.JPG
 
Last edited:

Bob NH

In the Trades
Messages
3,310
Reaction score
9
Points
0
Location
New Hampshire
The Square D interlock kits are about $70 on E b a y.

QOCGK2C for a QO panel.

It is a nice setup because you don't have to mess with rewiring your panel and all of the circuits are immediately connected to the generator.

You do have to manage your load so you don't overload the generator.

The problem with a small transfer switch is that it's a pain figuring out which circuits you are going to need on the generator, and the transfer switch can't switch the whole utility source off the panel, so the loads you want on the generator must all be on a subpanel.

My generator has the option of delivering full power as 120 Volts, all in phase. I set it up to do that so that I don't have to worry about trying to balance 120 Volt loads between two separate phases and I can run any 120 Volt circuit in the house (but no 240 Volt circuits). CAUTION: If you do that you must carefully manage any Multiwire Branch Circuits so you don't overload the neutral.
 
Last edited:

joe in queens

New Member
Messages
35
Reaction score
0
Points
0
I've been hearing those "whole house" configurations with small generators will most likely be "outlawed" in the next NEC code cycle (2008).

It seems they think we're incapable of managing loads on our own, and will run each and every light and appliance during an outage. If this trend continues, before long the genset will have to be matched to the service rating... typical 200A service will require a 48Kw genset to be compliant.

All this new requirement is going to do is ensure more jobs won't be filed, and dryer plugs will be used to backfeeed panels.

I too hate the idea of a sub-panel and having to chose what to do with and without... outlets not working, appliances not working, etc. And even with a sub-panel properly configured for an estimated load, the genset can still be overloaded.

Briggs and Stratton has some exciting new products for the home market, like their load management controller - it'll only switch on large loads if there's enough generator capacity to spare, this way critical loads are maintained, and optional loads will come online if available. Best of both worlds.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
joe in queens said:
I've been hearing those "whole house" configurations with small generators will most likely be "outlawed" in the next NEC code cycle (2008).


Only with a Automatic Transfer Switch, Manual will be fine...
 

Mike Swearingen

New Member
Messages
621
Reaction score
3
Points
0
Location
On Albemarle Sound In Northeastern NC
Website
www.albemarle-realty.com
Connection Hub Alternative

I'm not a pro electrician so I won't try to join the technical discussion here, but I went with this Connection Hub system from our power company rather than with a transfer switch and separate panel. Performs the same safety and performance duty on up to 12,000 watts on a 100-200 amp existing panel.
http://www.dom.com/products/generators/hub.jsp
I only have a 5500 watt portable generator, so I can run all of the 120v breakers only in my existing panel, or turn them all off and turn only the 240v breaker for the water heater on when we need hot water.
The device automatically turns off the (generator) power for 30 seconds and then switches to the line power when it is restored to alert you to turn off your generator.
The generator just plugs into the Connection Hub which is on the meter base. Easy, fast installation. Less expensive than a turnkey transfer switch and separate panel here. The longest that I've used it was 10 days for Hurricane Isabel in 2004. Works like a charm using the existing panel. I can operate everything but the central electric heatpump, one way or another, for our all-electric home on our 200 amp panel.