    When my A/C comes on, I get a flicker in my lights. What kind of issues should I look for? Loose wiring, incoming power problem........

  2. #2
    Plumbing Designer FloridaOrange's Avatar
    Join Date
    Dec 2005
    Location
    SW Florida
    Posts
    1,317

    Default

    I'm sure the electrical gurus could help you more but....
    When your AC comes on the condensor startup is pretty substantial. There are devices that can make your startup "easier". I've got one on my house and it's called a soft start. Geez Frank, could've asked me or hammer at the "other" place.

    That's where I would start anyway.
    Matt
    Semi-professional plumbing designer
    Enjoying life in SW Florida

  3. #3
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default flicker

    All of the above as starters, then a failing utility main feed, or a failing transformer, etc.

  4. #4
    Maintenance Mechanic RED BARN's Avatar
    Join Date
    Aug 2007
    Location
    Georgia
    Posts
    5

    Default

    Quote Originally Posted by FloridaOrange
    I'm sure the electrical gurus could help you more but....
    When your AC comes on the condensor startup is pretty substantial. There are devices that can make your startup "easier". I've got one on my house and it's called a soft start. Geez Frank, could've asked me or hammer at the "other" place.

    That's where I would start anyway.
    To be honest I figured it would be related to wiring or incoming feed problem from power provider. I will check into this "soft start", I've got an Uncle who does A/C work, maybe he can help obtain one.

    Thanks FO.

  5. #5
    Electrician Chris75's Avatar
    Join Date
    Aug 2007
    Location
    Litchfield, CT
    Posts
    608

    Default

    Most dimming of the lights is normal, the cause is related to the voltage drop from the startup of the motor, Not sure how much your lights are dimming so not sure if it is a serious problem or not, but if lights are dimming from using smaller appliances then you could have a loose neutral.

    Other things to look at is the wire size and distance they used to wire the outdoor unit, other than that add a soft start kit as stated above...

  6. #6
    DIY Senior Member BrianJohn's Avatar
    Join Date
    Jun 2007
    Location
    VA
    Posts
    151

    Default

    Stock response from previously answering this question.

    First you should check for possible connections issues, particularly if this problem just started.

    Light flicker (dimming and restoration of light to near preflicker level of lights from motor inrush) is a byproduct of several factors and generally is difficult to over come.

    AC motor loads (in particular compressors) but all motor loads have inrush currents. These inrush currents result in voltage drop in the branch circuit, panel bus, service laterals, utility transformer and possibility the utility HV feeders.

    Flicker is in addition user dependent; some people are more susceptible to flicker. For some reason flicker seems to bother women more that men (based upon personal experience).

    A Voltage Drop (VD) as little as 3 volts on a nominal 120 VAC system is noticeable (by me), 2.5% VD.

    We have had cases were the VD was all a byproduct of primarily single phase 120 VAC loads, in these cases we were able to put the lighting on L1 and all the motor loads on L2, the HVAC compressors were something the homeowner had to live with. This minimizes the flicker.


    To test for this VD and resulting flicker to determine the source of the inrush, use a min max amp clamp and min max multimeter at the main service watch the lights(it may take two workers) and correlate to the meters.
    Last edited by BrianJohn; 08-26-2007 at 05:33 AM.

  7. #7
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    Testing for VD? Maybe refer this to Dr. 90210???

  8. #8
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default Vd

    Maybe a penicillin shot will help the VD.

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •