Speedy Petey
Licensed Electrical Contractor
Yes. That is exactly right.hj said:In that case there were a "jillion" electricians who did not know what they were doing, including the one that wired my new house 6 years ago, to match my 3 prong male plug.
If the electrician who wired your house wired the dryer circuit to match the plug then I'd love to see what else he did there. You match the plug to the receptacle, NOT the other way around. And the receptacle MUST be wired to code.
If he installed a 3-prong dryer circuit and receptacle six years ago he obviously did NOT know what he was doing. That or he simply didn't care. The neutral/ground bond exception was dropped in 1996. Four prong receptacles with a separate ground and neutral have been mandatory since then.
If he EVER wired a dryer with 10/2, ESPECIALLY as soon as six years ago, I'd love to know his name so I can report him to the licensing bureau.
You are misunderstanding what I am saying. I am NOT saying 3-prong dryer receptacles were not legal or safe. That WAS the standard for MANY years. I see them all the time. Only I mostly see them wired with 10/3 without ground or SEU cable. The old, yet CORRECT way.hj said:As I said, it was standard for decades.
Not true. 4-prong receptacles have always been code for dryers and ranges in mobile homes.hj said:You never saw a 4 prong plug for a dryer until the last decade at the earliest.
Nice try.hj said:Maybe you are too new in the business to go back that far.