NO! Expensive and more work.
Use a plain 60A non-fused "pull-out" type disconnect. The type used for A/C installations. They are fully self contained and run about 10 bucks.
|
|
|
I'm moving my water heater and I guess i will need a disconnect at the new location. So i'm thinking a metal box with a double pole single throw 30 amp switch will do. Am I close?? Thanks!!
NO! Expensive and more work.
Use a plain 60A non-fused "pull-out" type disconnect. The type used for A/C installations. They are fully self contained and run about 10 bucks.
Or
Use a lock out on the breaket for about $2
Or
Maybe he's moving the heater next to the panel so he would not even need a separate disconnect...![]()
No it will be a good ways from the panel. I was checking out the disconnects that Speedy mentioned at the depot and they look like a pretty good deal . They had a 30 amp and a 60. I guess the 60 is recomended because the breaker will be 30a.?? Thanks for the replys.Originally Posted by Chris75
By definition, it would seem that if you have a 30A breaker, the disconnect would need to be rated for at least 30A; I think the 60A isn't needed. If I understand this, it's sort of like sizing the wiring, you can't use less than 12g on a 20A circuit, but 10g would be overkill...why spend the money unless you have a very long run.
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer
Originally Posted by jadnashua
60 amp disconnect is a pretty common thing you will find in a home center, and cheaper than a 30 amp...
Sounds like a plan, then. I was just figuring the 30A would be cheaper, and was all that was required. Must be a volume thing...
Jim DeBruycker
Important note - I'm not a pro
Retired Defense Industry Engineer
Originally Posted by jadnashua
Yep... Not really even sure why they make a 30a...
I would run 10/3wground from your main panel ,install new 30 amp brkr
unless you need to upgrade your service and panel.
I'm not sure what this has to do with the original question about needing a disconnect.Originally Posted by cwhyu2
Also, 10/3 is NOT needed for a water heater. 10/2 is perfect and typical for this installation.
Using 10/3 is basically wasteful.
How about the idea that (smart) water heaters of the future might requie a neutral?? Just remembering the days when we ran 10-2 for dryers....Originally Posted by Speedy Petey
I did price out a roll of 10-2 and 10-3 the other day. More than a water heater.![]()
Anyone that builds a "smart" water heater that requires a neutral or a 120 Volt circuit has proved that he is not smart enough to build a "smart" water heater.Originally Posted by hammerslammer
Right. I was just wondering if it might be "smart" to run a nuetral...Originally Posted by Bob NH
22 years ago my plumbers tried to talk me out of lowboy gas heaters in the crawlers. I was too "smart" to listen to them.I'd like to get this chit right in case i last another 22.
10-2 was never allowed for a dryer...need a insulated neutral.... You were allowed to use the neutral as a ground, but not the other way around...Originally Posted by hammerslammer