    Default Need guidance on new outdoor outlet

    It's time for me to get around to installing an outdoor outlet at the front of the house for seasonal usage: small water pump for the fountain, leaf blower and Christmas lights. I'd like the GFI outlets switched so that the fountain does not have to be plugged/unplugged twice a day. I'd prefer one of those weathertight boxes that cover the line cord while it is plugged in, in case of splashing. I'm looking for guidance on the best way to do this, what materials to use, and of course, code compliance.

    My first thought was to install a box on the decorative brick wall, at the yellow X, since there is an outlet in the living room on the other side. But the wife suggested putting it on the white siding so it is not as obtrusive, and I agree.

    On the other side of the siding is the interior wall of the foyer, and there are no switches or outlets in that area. However, I think I can drill a hole at the bottom of the siding, about 2" up from the concrete at the red X, and it will go into the crawl space (the floors are 8" higher than the concrete). From there I could run 12-3 Remulak (official wire of the Coneheads) to a junction box under the house. The weathertight box would have to be higher up, since the patio gets pressure washed or hosed off occasionally.

    So, how would you do this one? What does the code say about minimum and maximum height, and what would I use to go from the hole in the rim joist/siding to the box? What wire is permitted? Any suggestions for the GFI or weathertight box?

    Thanks,
    Walt

    Name:  Outdoor-Outlet-Location-005.jpg
Views: 1182
Size:  58.3 KB

  2. #2
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    It it were my job, I would install the box in the brick so that the front of the box is flush with the brick and only the in-use cover is sticking out. The circuit should originate from the main panel. I would run a 20A branch using 12/2 WG NM cable. How it is wired will depend on where the switch will go in the circuit and how access is through the walls.

    The box and receptacle must be weather resistant, and there must be an in-use cover installed on the box.

  3. #3
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Why would you want to run 12/3?

  4. #4
    DIY Junior Member TubeGuru's Avatar
    Join Date
    Aug 2010
    Location
    Redmond, WA
    Posts
    11

    Default

    Quote Originally Posted by dlarrivee View Post
    Why would you want to run 12/3?
    No reason other than that I have a spool of it on hand.

    I just got back from looking at in-use covers and boy are they big. A flush-mounted box looks like a given, unless I forgo the in-use concept and use a dual-gang flip-lid cover. I may not have been clear above that I was planning to put the switch and receptacle in the same box.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    Much better to install the switch inside...then, you don't have to go out at night to see if you actually shut things off! Or, at least higher up on the wall so you don't have to bend over to check and flip it.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6
    Test, Don't Guess! cacher_chick's Avatar
    Join Date
    Jan 2008
    Location
    Land of Cheese
    Posts
    3,142

    Default

    It is my understanding that the in-use cover is now required by code.

    I don't think you will find a switch/receptacle combo that is WR rated.

    I would put the switch on the inside and a single-gang box in the wall.
    Last edited by cacher_chick; 04-08-2012 at 08:35 PM.

  7. #7
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    I agree, set out a new circuit for this purpose if that is at all practical. The exterior receptacles need to be GFI protected. This can be accomplished with a breaker in the panel, and that will allow some flexibility at the receptacles.

    You could have two solid state timers feed by the line, and each of them switching some receptacles, or each switching half of a receptacle.

    These things are getting pretty sophisticated. You could have one timer for the fountain, and the other for the Christmas lights.

    I am pretty sure that "in use" covers are required in all jurisdictions, but I would not say that for a fact. I know I need them here.

    Certainly cutting a recess into the brickwork to sink a box would be the most professional approach. And it will be a fair bit of work.

    There is a requirement for how high an exterior receptacle must be mounted. Some people are brilliant at surfing the code and finding the references. I am not one of them. I understand that the requirement is 12" minimum. I have never had a problem with that.

  8. #8
    DIY Senior Member kreemoweet's Avatar
    Join Date
    Sep 2009
    Location
    Seattle. WA
    Posts
    371

    Default

    Unless the code provision has changed fairly recently, at least one receptacle outlet not higher than 6 1/2 feet above grade is required
    at both front and rear of a dwelling unit. There is no minimum height that I am aware of. I have seen receps installed below grade, in a
    window well, no problem.

  9. #9
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,390

    Default

    You don't want to have it sitting below the snow level, but not sure if that's an issue in Redmond.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  10. #10
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by kreemoweet View Post
    Unless the code provision has changed fairly recently, at least one receptacle outlet not higher than 6 1/2 feet above grade is required
    at both front and rear of a dwelling unit. There is no minimum height that I am aware of. I have seen receps installed below grade, in a
    window well, no problem.
    That is for new construction. There is no requirement that older residences be retrofitted to that standard.

    And I have installed several receptacles right up by the eaves on timers specifically for xmas lights. Keeps the cords from stringing all over the place.

  11. #11
    DIY Senior Member dlarrivee's Avatar
    Join Date
    Jun 2009
    Location
    Canada
    Posts
    1,172

    Default

    Since when are updated codes STRICTLY for new construction...?

  12. #12
    DIY Senior Member Homeownerinburb's Avatar
    Join Date
    Jan 2012
    Location
    Los Angeles, CA USA
    Posts
    505

    Default

    Quote Originally Posted by dlarrivee View Post
    Since when are updated codes STRICTLY for new construction...?
    In this case the update of the code does not force anyone to change existing installations.

    Tubeguru could chose to put in an outlet at the front of the house, pull a permit and get an inspection, and he will not need to install one in the back.

    Look for discussions of three wire installations of circuits for electric stoves and dryers. Until the mid '90's is was standard and practice to use the same conductor as the ground and the neutral. There is a small current returning down that line, the power for the stove light and the clock, I suppose. The heating elements are 240v.

    One can buy a new stove and install it with a three wire cordset if the existing arrangement is three wire. But current construction requires a four wire arrangement with the ground and neutral separate and not bonded at the stove. If you were to remodel the kitchen and move the outlet for the stove, you would be expected to replace it with a four wire arrangement.

    Classic grandfathering.

    For that matter, if your home has no GFIs in it, the fact that the code has required them for decades in new construction and remodeling does not mean that you are forced to go out and buy some today. Even if a receptacle failed and you wanted to replace it, you could use a conventional receptacle. Assume that your home required six to be compliant. YOu could install one, and there would be no need to install the other five.

    Requirements for grounding have evolved. If a residence has a panel that was installed in 1940 it almost certainly does not have grounding that matches today's code. Nothing would be expected of the homeowner until he replaces the service panel. Then the inspector would insist on a compliant grounding system.
    Last edited by Homeownerinburb; 04-09-2012 at 12:26 AM.

  13. #13
    Jack of all trades DonL's Avatar
    Join Date
    Mar 2011
    Location
    Houston, TX
    Posts
    3,644

    Default

    "Why would you want to run 12/3?"

    Then it would be electric car ready ?

    Put a lock box so people do not steal your electricity, or put the switch inside.
    Theory only works perfect in a vacuum.

    Cyber Security Protection for Windows C:\ > WWW.WinForce.Net

Similar Threads

  1. Replies: 9
    Last Post: 12-11-2012, 12:01 PM
  2. Need DWV Guidance
    By Ryan_Z71 in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 04-26-2010, 01:39 PM
  3. adding outdoor outlet under deck
    By DanMc in forum Electrical Forum discussion & Blog
    Replies: 7
    Last Post: 01-19-2010, 05:26 AM
  4. New toilet guidance
    By Mike1399 in forum Toilet Forum discussions
    Replies: 5
    Last Post: 08-29-2009, 07:20 PM
  5. Replies: 9
    Last Post: 07-18-2008, 07:16 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •