    Default venting of utility sink pump in basement

    I bought and installed a utility tub and Flotec "laundry tray system" (sump pump in a box): the cesspool line is a few feet above the basement floor. Installation went well: the pump cycles correctly, the tub drains.

    However, when I went to install the Oatey "in-line vent" in the vent hole of pump box I wound up thinking about the operation of the vent in this application. It seems to me that the inline-vent can NOT be used because the incoming water will attempt to compress the air in the box due to the one-way air flow of the in-line vent.

    Is this true?

    If so, is there any way of avoiding running a vent pipe to the outdoors?

    Thanks ahead of time!

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    23,534

    Default vent

    That is true, and if the sink has its own trap before going into the tank it may "never" drain. There is no "proper" way to install the vent without it either tying into an existing vent, (not a drain line), or going out through the roof.

  3. #3
    DIY Junior Member
    Join Date
    Jul 2005
    Location
    Long Island, NY
    Posts
    2

    Default basement laundry & utility sink vents

    I am planning to put laundry and sink to the basement.

    What is the simple solution for this pump box problem? If you only have relatively clean water waste I think you don't need a P trap on the sink or anything hooked up to the box vent, just pump to a P trap on the drain side, like for the washer.

    If the water is nasty, you want a trap but now hj are you saying you need the box vent to go both ways? (both in and out?) That sounds strange. Can't you "compress" the air to the drain, possibly through the pump?

    If it's not possible to use an air admittance valve for this application, I suppose while I'm cutting a dryer vent hole in my foundation I should go ahead and cut a sink pump vent too? Maybe I can seal up the washer drain and vent it this way as well.. Any advantage to that?

    Thanks in advance for your help!

  4. #4
    DIY Junior Member
    Join Date
    Jul 2005
    Location
    Long Island, NY
    Posts
    2

    Default

    By the way vkristof@optonline.net told me in email that he went ahead and built it and the air admittance valve worked fine. He suggests maybe the box is not tight enough to allow the compression to be a problem.

    So at this point I am really only concerned about keeping down the stink, and whatever the codes say. If there are better solutions, maybe we can find them. Obviously this topic is very popular but poorly understood. Any daredevils out there with stories to tell?

  5. #5

    Default

    Hmmmm...I have the same issue. What if you cannot tie into a vent. How do you solve?

  6. #6
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,460

    Default

    Its really simple! These pump systems require 2-way airflow to work. This means the Air Admittance Valve is not an option. You need a vent that goes through the roof! By code it is your only option. You may tie into an existing through the roof vent to accomplish this. Leaving the system open is not an option as it is a drain and smells will occor. If you cannot find a way to properly vent this then you need to hire a plumber who can!

    Codes are here to ensure that plumbing works properly and your health is no endangered.

    BTW The Flotec pump is the last pump I would consider using. It has an inlet strainer that is very prone to clogging.
    Last edited by Redwood; 03-24-2008 at 08:20 AM.

  7. #7

    Default What about this utility sink pump?

    http://www.*********.com/webapp/wcs/...10000003+90001

    If the link does not work it refers to:
    Flotec
    Utility Sink Pump
    Model FPUS1860A

  8. #8
    DIY Member littlebrook's Avatar
    Join Date
    Aug 2008
    Location
    Rochester, NY
    Posts
    62

    Default

    Quote Originally Posted by jzsjr View Post
    http://www.*********.com/webapp/wcs/...10000003+90001

    If the link does not work it refers to:
    Flotec
    Utility Sink Pump
    Model FPUS1860A
    I have a similar type of pump on my laundry tub but made by Bur-Cam. It works well and doesn't need a vent but I think you'll find the pro plumbers on this forum will not recommend it for various reasons.
    Last edited by littlebrook; 12-26-2008 at 06:52 PM. Reason: typo

  9. #9

    Default venting utility sink

    I have the same set up, drain pipe above the basement floor. The plumber wants to connect the vent from the utility sink pump - not to the roof vent - but to the one that goes out of the foundation of the house about a foot off the ground. Is this ok?

  10. #10
    Master Plumber Redwood's Avatar
    Join Date
    Dec 2007
    Location
    Connecticut
    Posts
    7,460

    Default

    If side venting is allowed under code in your area then it is...

    Most don't.

    I don't get what is so hard about getting a vent through the roof...
    Maybe you need better plumbers...