Cost to have gas line ran to stove?

Users who are viewing this thread

enviroko

New Member
Messages
37
Reaction score
0
Points
0
Hi, can anyone give me a ballpark figure for having the following job done?

We currently have an electric stove but our natural gas line runs directly under (full basement) the stove and we plan to switch to gas. So all that I believe needs to be done is to tap into this line and run a line up through the floor to the stove.

I want to have someone come in and do it to make sure that is to code but I don't want to get taken.

Thanks!
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
Too many unmentioned variables there.
Joist direction...any drilling?, gas main size & number of BTU's attached vs length, availability for connection to the main...will it need to be threaded? or is there a tee available?
Best to get a couple of estimates...or take pics, post them and hope we can see whats there.


Could be a $150 quicky, could be a whole day $1,000+....
 

enviroko

New Member
Messages
37
Reaction score
0
Points
0
* The pipe is 1" OD & very easily accessable.
* Runs parallel to the joists but it needs to move one joist over to go up through the floor behind the stove. I will drill hole before the plumber comes in.
* The pipe has no T, pipe will need to be threaded. It is currently a straight pipe that runs right on past the stove area.
* BTUs I don't know.
 

Statjunk

DIY Senior Member
Messages
540
Reaction score
0
Points
0
I'm no expert but I did sleep at a Holiday Inn last night.

I'd say between $250 and $500.

Tom
 

Tjbaudio

Member
Messages
167
Reaction score
0
Points
16
Location
Las Vegas NV
enviroko said:
* The pipe is 1" OD & very easily accessable.
* Runs parallel to the joists but it needs to move one joist over to go up through the floor behind the stove. I will drill hole before the plumber comes in.
* The pipe has no T, pipe will need to be threaded. It is currently a straight pipe that runs right on past the stove area.
* BTUs I don't know.
I would let the plumer do the drilling. He/she may drill first or may get the T in and then drill to where it ended up. You want the min size hole you can get. Drilling first and then having to ream out the whole would suck. Also what if you slip and cut the pipe? Probably wont damage it too bad but it may make for a problem. All in all I think the drilling is the minimal part of the project. You wont save much time of money and may cost extra!
 

Markts30

Commercial Plumber
Messages
625
Reaction score
1
Points
0
Location
Phoenix, AZ
What else is being fed by this line?
You can only run so many BTUs on a given length of 1"...
Does your water heater, clothes dryer, furnace, bar-b-que etc run on the same line?
How about a gas fired pool heater etc...
Once you know how many BTUs you are drawing from that line, you can figure if the new fixture will overtax it (some gas ranges can run upwards of 85-100,000 BTUs though most are less)
A 1" pipe with the furthest fixture having 80' of pipe to it can only support 222,000 BTUs
As well, be aware that cutting a t into the middle of an existing gas line is going to be a pain... The plumber is going to have to use a left and right nipple and the whole system will likely have to be re-tested and inspected if the work is going to be permitted (I would advise to have a permit pulled and inspection done...)
 
Last edited:

Cwhyu2

Consultant
Messages
1,615
Reaction score
22
Points
38
Location
Cincinnati OH
trak pipe

Trak pipe is the way I would go.But you need to have someone trained
to install this product.Look it up.
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
cwhyu2 said:
Trak pipe is the way I would go.But you need to have someone trained
to install this product.Look it up.

Here lies the irony, I'm certified in tracpipe and wardflex (like thats a big deal).
I still prefer hard piping over it.
 

Lee Polowczuk

New Member
Messages
63
Reaction score
0
Points
0
Location
Florida
i once had this done... listen to this....

i called the plumber.... and he started dragging out this very thick book.. looked at my project... started doing all this estimating stuff.... came up to 1300.

i said thanks... somehow i got taken for 35 dollars for the estimate.

called the gas company.... done for 225.


second house.... had a friend do it... about 150 including materials..

both of these jobs were very similar... under house access two runs with a couple of 90's.

both were black pipe... code here allows flexible...but i wanted black pipe
 

hj

Master Plumber
Messages
33,602
Reaction score
1,040
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
gas company

Our gas company is NOT ALLOWED to do any piping after the meter, regardless of the amount. And they value their cushy jobs too much to rist side jobs.
 

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Don't forget you will need an electrician to add a 115v receptacle for the gas stove... unless you were going to do that work yourself...
 

Jadnashua

Retired Defense Industry Engineer xxx
Messages
32,770
Reaction score
1,190
Points
113
Location
New England
If you go with a dual-fuel stove, then you'd need 240vac...while you're at it, another circuit for a vent hood, and maybe more to bring the room up to code while you're at it.
 