    Default Electrical code on Busway to a water line

    Can someone tell me what the code is relating a 600v busway and the distance from a water line? The busway is not water tight.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    There no requirements in the NEC for a distance from water lines

  3. #3
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    There is no specific clearance that I know of.
    Are you concerned the pipe will burst?

    Water lines do not pose any specific threats to electrical equipment. Folks are amazed when they hear there is not a ton of clearance required between water piping and electrical equipment.

  4. #4
    Maint Mrr/electrician Randy T's Avatar
    Join Date
    Aug 2007
    Location
    Houston,TX
    Posts
    3

    Smile

    Quote Originally Posted by jwelectric
    There no requirements in the NEC for a distance from water lines

    Thanks for the Info, I went thru the code book & could not find anyting on this subject. We are getting ready for a Final and the ast thing I need is to create a Red Tag.

  5. #5
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,638

    Default code

    In that case, you should have asked the question a long time ago, not when the job is done and the inspector is walking up to the door.

  6. #6
    Maint Mrr/electrician Randy T's Avatar
    Join Date
    Aug 2007
    Location
    Houston,TX
    Posts
    3

    Default

    Quote Originally Posted by hj
    In that case, you should have asked the question a long time ago, not when the job is done and the inspector is walking up to the door.

    I did not know the job was going to be mine until this week. I don't get much notice around here. That has been my loudest arguement about this place.

  7. #7
    DIY Senior Member BrianJohn's Avatar
    Join Date
    Jun 2007
    Location
    VA
    Posts
    151

    Default

    Speedy:

    The number ONE reason for busway failures is WATER. The number one reason burst pipes, over flow of floor drains and toilets and slop sinks overflowing.

  8. #8
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by BrianJohn
    The number ONE reason for busway failures is WATER. The number one reason burst pipes, over flow of floor drains and toilets and slop sinks overflowing.
    So then why is there no code required separation between pipes and bussways?

    Obviously toilets and floor drains are not a concern.

  9. #9
    DIY Senior Member BrianJohn's Avatar
    Join Date
    Jun 2007
    Location
    VA
    Posts
    151

    Default

    The NEC does not always have rules that fit all problems. In addition this would be VERY difficult to implement, making busway less than acceptable based upon the added cost of isolation. In addition moving water pipes would do minimal as when water pipes break water goes where it pleases, I have seen little contractors can do to stop it. In addition I can only tell you what I have experienced, what manufactures, insurance companies and forensics electrical engineers I work with tell me.

  10. #10
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    The way you are thinking is that the water pipe was installed with a flaw.

    The water pipe is not installed so it will burst but instead it is installed to handle the pressure applied.

    Should it burst it would be no diffferent than installing a buss under a roof that might leak.

    Using you way of thinking I suppose that the duck would need to be installed at least one floor down in case the roof started leaking.

  11. #11
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Quote Originally Posted by jwelectric
    The water pipe is not installed so it will burst but instead it is installed to handle the pressure applied.

    Should it burst it would be no diffferent than installing a buss under a roof that might leak.
    Pretty much my thinking as well.