    Default Electrical code on Busway to a water line

    Can someone tell me what the code is relating a 600v busway and the distance from a water line? The busway is not water tight.

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    There no requirements in the NEC for a distance from water lines

  3. #3
    Maint Mrr/electrician Randy T's Avatar
    Join Date
    Aug 2007
    Location
    Houston,TX
    Posts
    3

    Smile

    Quote Originally Posted by jwelectric
    There no requirements in the NEC for a distance from water lines

    Thanks for the Info, I went thru the code book & could not find anyting on this subject. We are getting ready for a Final and the ast thing I need is to create a Red Tag.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default code

    In that case, you should have asked the question a long time ago, not when the job is done and the inspector is walking up to the door.

  5. #5
    Maint Mrr/electrician Randy T's Avatar
    Join Date
    Aug 2007
    Location
    Houston,TX
    Posts
    3

    Default

    Quote Originally Posted by hj
    In that case, you should have asked the question a long time ago, not when the job is done and the inspector is walking up to the door.

    I did not know the job was going to be mine until this week. I don't get much notice around here. That has been my loudest arguement about this place.

  6. #6
    DIY Senior Member BrianJohn's Avatar
    Join Date
    Jun 2007
    Location
    VA
    Posts
    151

    Default

    Speedy:

    The number ONE reason for busway failures is WATER. The number one reason burst pipes, over flow of floor drains and toilets and slop sinks overflowing.

  7. #7
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    There is no specific clearance that I know of.
    Are you concerned the pipe will burst?

    Water lines do not pose any specific threats to electrical equipment. Folks are amazed when they hear there is not a ton of clearance required between water piping and electrical equipment.