you might have slow drain or stoppage.
|
|
|
If I untwist one of the Oatey Air Admittance valves under either the main kitchen sink or the island sink the sink drains normally. Otherwise I hear gurgling, usually in the island sink. I put a plastic bag over the AAV pipe and unscrewed the AAV, the bag filled with air when I ran the sink. Isn't an AAV supposed to allow air in, not out? What is the likely problem?
Mark
you might have slow drain or stoppage.
It could be the AAV going bad....
but their is a better chance that the drainline is
beginning to get stopped up.....
probably need to clean it out and see if that solves the issue
YOu are correct in that the AAV lets air in, but not out. That is your problem. Air is being trapped in the pipe, and since the air cannot be vented because of the AAV, the water either cannot drain, or cannot drain very fast.
mdistel,
If you don't hear a suctioning sound while the vent is in place...replace it.
Look for a "Studor" vent.
If the problem where positive pressure, you'd likely have overspill when the vent were removed.
You could do a simple test by putting your hand over the hole while the sink is draining.
"The biggest regrets we have in life are the chances we never took."
That's not making sense to me, Grumpy.
If the bag's filling with airl... by definition... that's positive pressure, isn't it?
Are you using those words in some specialized, plumber-ese, technical sort of way or something?
Master Plumber Mark:
there is nothing better than the
manly smell of WD 40 in the air
while banging away on brass with a chisel and hammer...
it smells like......victory......
do not hit your thumb...
__________________
Just so everyone's clear: I'm the POODLE in the picture ("french", get it?) The hot woman is my wife.
There's likely a mechanical vent there because the drain drops into the floor after the trap.
When the waste water drops, it creates a suction...not positive pressure...without a vent for the vacuum it drains slower.
"The biggest regrets we have in life are the chances we never took."
He already stated that there is an AAV. Suction/vacuum speeds up drainage. Vents stop vacuum thus slowing drainage rate down to whatever the water's head pressure will generate. Positive pressure slows or stops drainage.
I missed the part about the bag filling...geesh.
Ten to one the drain is either undersized, or blocked.
Last edited by GrumpyPlumber; 08-16-2007 at 09:44 AM.
"The biggest regrets we have in life are the chances we never took."
Also...why wasn't the island bow vented?
"The biggest regrets we have in life are the chances we never took."
Thank you for all the replies. Both the island and the main sink are vented. I'll have to have a plumber come sank the lines, I tried and didn't get anywhere. Now I need to find a good plumber in the Cleveland area.
Mark
For the same reason AAV's are used anywhere. It is cheaper. But if the drain line is plugging, then a bow/loop vent will give the same symptoms as an AAV.
Right, I keep forgetting mechanical vents are allowed in some states.Originally Posted by hj
Here bow vents are an art...we take pride in them.
If this work was done on the cheap, then I'm putting my money on the common drain being 1-1/2", maybe 1-1/4".
"The biggest regrets we have in life are the chances we never took."