Hi. I have a pump that run with the usual 30/50 settings. I have to put some air in the tank a couple of times a year and everything is fine.
This week, the pump begin to kick in very low, below 10. I don't know why. I was thinking of the usual air in the tank problem.
I've cheched air pressur ein the tank and put it as usual:28psi.
But now the pump kicks in below 10 near zero and stop at 68.
I've tried to ajust the control switch without succes.
A weird thing happens when pressure goes off of the system, let's say after a flush. When looking to the meter, the pressure goes down slowly down to 30 psi and all of a sudden drops to 10 and less. So I can't adjust the control switch because I don't have my 20 psi gap between the kick in and tyhe kick out.
Any idea?
Thanks
This week, the pump begin to kick in very low, below 10. I don't know why. I was thinking of the usual air in the tank problem.
I've cheched air pressur ein the tank and put it as usual:28psi.
But now the pump kicks in below 10 near zero and stop at 68.
I've tried to ajust the control switch without succes.
A weird thing happens when pressure goes off of the system, let's say after a flush. When looking to the meter, the pressure goes down slowly down to 30 psi and all of a sudden drops to 10 and less. So I can't adjust the control switch because I don't have my 20 psi gap between the kick in and tyhe kick out.