water heater venting

Users who are viewing this thread

perrycat

New Member
Messages
39
Reaction score
0
Points
0
Is there any online charts that anyone knows of for sizing flues ( not the chimney) based on btu's? I know it's in the code book, but I don't have access to one recently my copy got "vanished". It's just something my boss said he was going to start asking in our meetings, asking people questions related to gas sizing and water heater flue sizing questions. I'm not a full journeyman.....yet.
In one state you have to upgrade the flue to 4", in another you can still use 3" on like a 50 gallon gas. Does anybody know why there's this difference?
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
It depends on whether your states uses the NFPA, IF so...you can download it online for about $35 from Techstreet.
I can tell you the formula for a common vent on gas fixtures, but there's a chart in the book for size vs BTU...maybe later I'll look it up.
Whatever ya do...NEVER change the MFG size.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
its just stupid politics at its very best....

In one state you have to upgrade the flue to 4", in another you can still use 3" on like a 50 gallon gas. Does anybody know why there's this difference?[/quote]

IAround here we can use 3 inch on a water heater except
for any type of city jobs around here. They force us to increase the size to
4 inch....on a standard heater....which means running
a new chimmney however far to make the inspectors happy


the stupid thing about it is the open hood vent on most
all water heaters reduce the size of the chimmney to 3 inch
right from the start at the flu hood.......

so basically.. you have restricted the vent right to 3
inch from the start


you could not run 4 inch from something and
reduce it down to three going into a chimmney,
they would jump up and down about that.

I hope that some inspector never realizes this
and tries to make everyone get larger hood vents for the
heaters to " pass code.." ..

they will argue that fumes could escape
out the bottom of the hood vent which is about 6 inch
before getting into the 4 inch pipe.


I dont think that they make them..or ever have.
 
Last edited:

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
In most cases, the controlling authority is the National Fuel Gas Code. That book is inexpensive, and available on line. It is a "must have".

Also, it is a code requirement that a water heater be installed in accordance with it's manufacturer's instructions. Generally, these call out the Fuel Gas Code as their reference, so there you go!
 

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
OK...it's in Ch. 13 of the nat'l fuel & gas code, I'm gonna let you look it up.
Also, law requires any manufacturer to include a copy of the code with the fixture.
So, you could simply look at the manual on the heater for your answer.
Perry...the sooner you aclimate yourself to the code book, familiarize yourself with rough memorization on what chapters have what info, the better off you'll be.
Once you get your license, looking up code isn't going to be to win arguments anymore...it'll be your livelyhood.
 
Last edited:

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
hj said:
"Look in the manual on the water heater"? Now isn't that a unique idea? I will have to try that sometime, not.


It's all over the code book..."Refer to manufacturer instruction".
The manufacturer has to be code approved obviously, but...you're kidding...right?
Any inspection I've done on a boiler/water heater..etc, the inspector wants the manual there so he can see what the specs call for.
You didn't know this?
In my state (and likely most) the MFG is legally obligated to include an actual copy of relative code as well.
 

perrycat

New Member
Messages
39
Reaction score
0
Points
0
Thanks much

thank you all for the replies to that. I hate to say it but I've never really looked at the manual on most heaters except maybe powervents to see if what was there was going to work.

The upgrades, I was doing a little google type research, and what I've come up with is I think what they're worried about now is that there's something called "orphaning" of a chimney. The original chimney in a house with say a gas furnace or oil fired furnace....even old ones that had a coal furnace....the chimney was apparently sized for both, a furnace, and a water heater.... and now with more and more people going to these high output super high efficiency furnaces that are basically like a power vent water heater, and discharge out the side of the house, now the water heater is all alone with that great big space, and the cold air in winter apparently is more than just the water heater can overcome and the exaust gets pushed back down and backs up out the hood....I don't know if that really is why, but that's maybe why.

But I'm going to really learn all the gas stuff. I'm gonna look for that fuel gas book, thanks. You know, as much as a pain in the butt as it is to get licensed, keep up with all that etc...there's one thing, the more technical they get the less home owners and jack leg plumbers will be doing the work, the more business for plumbers.
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
perrycat said:
Is there any online charts that anyone knows of for sizing flues ( not the chimney) based on btu's? I know it's in the code book, but I don't have access to one recently my copy got "vanished". It's just something my boss said he was going to start asking in our meetings, asking people questions related to gas sizing and water heater flue sizing questions. I'm not a full journeyman.....yet.
In one state you have to upgrade the flue to 4", in another you can still use 3" on like a 50 gallon gas. Does anybody know why there's this difference?


The heaters in my area when they are 60 gallons or more, the flue diverter will automatically be a 4" flue diverter with no ability to size down.

In all applications....the flue chase of any water heater has to be matched, never decreased as it leaves the unit and heads to the B vent or chimney.

Those heaters with a 4" flue diverter only will have a 4" flue chase to the burner assembly, not 3".

I believe that anything above 55,000 BTU's requires a 4" flue...not sure on that but I know I'm close.

http://www.uscarb.com/natural-gas-chart.htm
 
Last edited:

GrumpyPlumber

Licensed Grump
Messages
1,521
Reaction score
57
Points
48
Location
Licensed Grump
Sounds 'bout right RUGGED, though linear distance has some effect on sizing...I'm usually reading up on boiler venting as opposed to heaters as switch outs are generally a straight shot..
Just to stress the importance of reading the manual...I once watched a fella take two days to dismantle a powervented 75 gal heater because it would fire up, then stop.
He tried "everything" he could think of and finally drained it down & dismantled it, called in an order for all new replacement parts.
I'd been on a house next door in the same complex (new) wrapping up the gas piping and testing, I finally went over to check in on him and..well...it wasn't good...there were parts everywhere.
I'd stopped in the first day and he snapped at me, I was new with the co, so I just went back to my own work...as instructed by the owner the day before. ("He isn't licensed, but this is his job, let him work alone")
I picked up the manual which he'd tossed to the side after looking up and seeing he had 2" PVC running to the sill from the heater...I knew what the trouble was, but he'd been very defensive so I'd kept my distance to this point.
I opened the manual to the "venting" section, where in BOLD lettering it stated "WARNING: DO NOT USE LESS THAN 3" DIAMETER VENTING".
He'd installed a few 40 & 50 gal power vents, but this was apparently his first 75.
Cost the company 2 days labor, I left not long after.
Thank GOD heaters and gas appliances come with so many safeties now.
 

Construct30

New Member
Messages
588
Reaction score
0
Points
0
Location
NorthWest PA

the stupid thing about it is the open hood vent on most
all water heaters reduce the size of the chimmney to 3 inch
right from the start at the flu hood.......

so basically.. you have restricted the vent right to 3
inch from the start


you could not run 4 inch from something and
reduce it down to three going into a chimmney,
they would jump up and down about that.

I hope that some inspector never realizes this
and tries to make everyone get larger hood vents for the
heaters to " pass code.." ..

they will argue that fumes could escape
out the bottom of the hood vent which is about 6 inch
before getting into the 4 inch pipe.


I dont think that they make them..or ever have.[/QUOTE]


Up sizing the pipe makes up for some elbows and longer runs to a certain degree. You see it a lot on furnaces and hotwater tanks. It makes better draft on that 3" take off, less drag on the way to the chimney. However inspectors can come up with weird stuff from time to time. If it doesn't matter I don't argue, but if it's flat out wrong...
 