    Default table or chart for AWG

    Anyone has a link for a chart for how many amps each AWG can handle in both Aluminum and copper? i am looking for something that can handle 60amp, 100amp, and 200amp
    thanks

  2. #2
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,655

    Default wire

    Single wire or 3 wire cable, and what is the length and ambient temperature?

  3. #3
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    Also, what is it being used for? A service gets sized quite differently from a branch circuit. As does an A/C or motor.

    There is NO blanket chart such as as you ask. It would be impossible and inaccurate.

  4. #4

    Default

    well i hired a contractor to run a 200amp and a 100amp into my 2 family house.
    and from what i can tell he is running a #4AWG alum wire for the 100amp main panel from the meter. I thought that wire is only rated for 60amp? The run is only like 4 feet from the meters to the 2 main panels. I just want to make sure he is running the correct wire and i wont have a problem when i start to pull 80 - 90 amps out of that panel because HVAC systems are going in next week. I live in NJ just out side of Manhattan.
    Last edited by hids2000; 07-27-2007 at 05:13 AM.

  5. #5
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    If it is being inspected like it should be the inspector will not pass it if it does not meet code.

  6. #6

    Default

    yes, the work will be inspected. It is more for my own personal info. If the contractor used a wire that is not up to code I would like to get that fixed while he is still here and i didn't give him the final payment yet. God knows if he will come back once he get all the money.

    This is what I can read from the side of the cable.

    (UL) 2 CDR AWG 2-1 CDR AWG 4 COMPACT ALUMAFLEX TYPE XHHW-2 CDRS 600 VOLTS (TM) AA8176
    Last edited by hids2000; 07-27-2007 at 05:31 AM.