    I am doing a 'minor' upgrade to part of my kitchen. You know the routine -- its a domino effect, where ruined subfloor, lead to ripping out counter, sink, and base cabinet along one wall, lead to redoing kitchen plumbing, lead to opening drywall to inspect for further damage, lead to running some new circuits.

    OK, here is my question. I want to add a couple of circuits to take some pressure off of the existing 15 amp circuit. One circuit for a couple of receptacles along the counter, and another circuit dedicated for the dishwasher. Since this is all on the same wall, I want to do a home-run back to the box with 12-3, and split it in the kitchen between the two circuits. Will this be considered balanced, or does it violate code? If so, am I better off with separate 12-2 home-runs?

    My wife thinks it has crossed the line to become a 'major' remodel. Something about not being able to function in a kitchen all torn up with no plumbing. I need answers fast, or my next project is to build a 'dog house' out in the garage.

    Thanks!
    DrummerDad

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    A multiwire circuit will do well for this installation. in the first box be sure to not cross the neutral from the 3 conductor and the diswasher with the load side of the required GFCI receptacle and every thing will work fine.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,399

    Default

    RUn two 12/2 circuits and don't worry about it. The neutral is only balanced if there is the same current in both hot leads, which won't likely happen.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    Quote Originally Posted by DrummerDad
    I am doing a 'minor' upgrade to part of my kitchen. You know the routine -- its a domino effect, where ruined subfloor, lead to ripping out counter, sink, and base cabinet along one wall, lead to redoing kitchen plumbing, lead to opening drywall to inspect for further damage, lead to running some new circuits.

    OK, here is my question. I want to add a couple of circuits to take some pressure off of the existing 15 amp circuit. One circuit for a couple of receptacles along the counter, and another circuit dedicated for the dishwasher. Since this is all on the same wall, I want to do a home-run back to the box with 12-3, and split it in the kitchen between the two circuits. Will this be considered balanced, or does it violate code? If so, am I better off with separate 12-2 home-runs?

    My wife thinks it has crossed the line to become a 'major' remodel. Something about not being able to function in a kitchen all torn up with no plumbing. I need answers fast, or my next project is to build a 'dog house' out in the garage.

    Thanks!
    Rather than running 12/3 just run 2 seperate circuits.

  5. #5
    General Contractor dx's Avatar
    Join Date
    Jul 2005
    Location
    Michigan
    Posts
    156

    Default

    Quote Originally Posted by jwelectric
    A multiwire circuit will do well for this installation.
    Disagree. Multiwire circuits are poorly understood by some electricians I know, let alone homeowners. It is crucial that the red and black be on different buses. Otherwise the neutral gets overloaded and is a fire hazard.

    Even if properly coached, a DIY may later forget the whole thing and move breakers around in the panel, ending up with both breakers on the same bus.

    Keep it simple and use 2 cables.