    Default Residential Wiring & Crimp Fittings

    I'm wiring an addition to my house.. I've been through this a few times in the past (actually rewired my current house a few years ago). I really like to use stranded wire since it is easier to pull (12 Ga THHN). I just find it annoying getting stranded wire around the screw connectors on outlets and switches.

    Is is accepted by code (2005 NEC) to use mechanical crimp lugs in the place of wrapping the wire around the screw connector? I can not find a reference on GB's site stating that they specifically conform to the 2005 NEC...

    Is this a crazy way to attach the wires?

    Thanks,
    Steve

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by seaneys

    Is this a crazy way to attach the wires?

    Thanks,
    Steve
    Yes

    Just leave a little piece (about 1/4 inch) of the insulation at the very end of the stripped end and it will hold the strands together when installing them under a screw

  3. #3
    Plumber jimbo's Avatar
    Join Date
    Aug 2004
    Location
    San Diego
    Posts
    9,001

    Default

    For receptacles, use the kind that are backwire. NOT back-stabbed. Use the kind where the end of the wire is pushed into an opening on the back, and when you tighten the screw it clamps the wire. Very secure .

  4. #4
    Architect Spaceman Spiff's Avatar
    Join Date
    Aug 2004
    Location
    Salt Lake City, Utah
    Posts
    277

    Default

    As long as the crimp on connector is UL listed for attachment to that type of wire you should be fine. If you look in the section that covers THHN/THWN it should say that any listed terminations are acceptable. Don't forget that UL listing requires that you attach per manufacturer's instructions. I've seen this in commercial wire-ups where they didn't use the back-wire (not backstab) receptacles as Jimbo suggests (best option).
    Spaceman Spiff aka Mike