    Default Plumbing question

    When connecting a 3" horizontal waste line from a toilet into the main 3" line using a combination fitting, what angle does the combination fitting have to be. Does it have to be positioned so it is 45 degrees or greater on the main line? Thanks in advance.

  2. #2
    Homeowner geniescience's Avatar
    Join Date
    Nov 2005
    Location
    humid summers hot, humid winters cold
    Posts
    2,152

    Default clarify

    catk9 believe it or not, your original question was even more confusing.

    What angle (how many degrees) does a combo make?

    Then, tell me please how that fitting is to be oriented in space so that it makes a 45 degee angle with something else oriented in space. Be real clear about what is horizontal and vertical and then, diagonal (or 45) with respect to what else. Please.

    David

  3. #3

    Default

    I will try to describe it better. The 3" ABS waste pipe from the toilet is dropping straight down thru the floor to a combination tee & wye. There is a clean out on one end of the combination and on the other end is a 6 foot section of 3" that is horizontal. The vent comes off between the toilet and the combination. The main waste line is running some what perpendicular to the 6' section of 3" pipe. I will be attaching the 6' piece to the main line using the comination tee & wye. The long sweeping part of the combination fitting will be connected to the 6' piece. At what angle does the combination fitting have to be when I connect them. Zero would be if it was laying on the ground and 90 degrees, it would be sticking straight up. Is this any clearer?

  4. #4
    Plumber BAPlumber's Avatar
    Join Date
    Jul 2007
    Location
    Vashon, Washington
    Posts
    227

    Default

    your drain lines need to have at least 1/4" per foot of fall, so your connection should maintain at least that. You could roll that combo on a 22, 45 or 90 (straight up and down) if needed.

    I'm still a little confused about your question, I hope this helps. Pictures are always great.

    Brent

  5. #5

    Default

    Thanks Brent. Yes it does help. I didn't know if I could roll the combination down to as far as 22. I thought there might be a code that said it had to be at the 45 or greater. If I can roll it over to 22, I can then get the required drop of 1/4 per foot. Thanks again.

  6. #6
    Jack of all trades frenchie's Avatar
    Join Date
    Dec 2006
    Location
    Brooklyn, NY and Fire Island, NY
    Posts
    1,244

    Default

    I think you're thinking of vent connections - they do need to be kept at 45* or steeper.

  7. #7

    Default

    Thanks frenchie.

  8. #8
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,195
    Blog Entries
    1

    Default


    You will need a wye fitting if it is on the horizontal.
    That is a 45 degree change of dirction.


    A santee is not right for that.
    You can use a santee, if you are going from horizontal to vertical.
    But not horizontal to horizontal.

    A combination fitting is like a wye and a 45 together.

    If the wye fitting or a combination fitting is used, you can tilt them like BAPlumber mentioned.
    Last edited by Terry; 09-15-2007 at 06:26 PM.

  9. #9

    Default

    Thanks Terry and everyone else for your help. I understand now.