Thread: running quick disconnect to central AC

  1. #1

    Default running quick disconnect to central AC

    I am installing an out door AC unit and need to run 220v 15 AMP power to it.
    My question is can i just use UF 12-3 wires directly from main panel through the wall into the quick disconnect than UF 12-3 into the AC. The run is about 6ft in length.

    Do I need to put the UF wire inside a conduit both before and after the disconnect?

    If I need to put the UF 12-3 inside of a conduit will a 1/2" metal conduit be big enough?

    thanks

  2. #2
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    For 15 amps #14 will be large enough.

    Yes the conductors will need protection from the disconnect to the AC unit but flex would be better than metal

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,434

    Default

    A condenser unit only needs 12/2 (no neutral) with ground. Don't have any ideas about code, but all of those I've seen are wired with a waterproof conduit from the shutoff to the unit.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4

    Default

    see the problem is i walked around and looked at other houses.
    Some of them are doing what I plan to which is using UF to the disconnect and UF to the AC.

    But some of them are using conduit from the house to the disconnect than UF after the disconnect to the AC.

    I guess i will have to call the building department up and ask them.

  5. #5

    Default

    Quote Originally Posted by jwelectric
    For 15 amps #14 will be large enough.

    Yes the conductors will need protection from the disconnect to the AC unit but flex would be better than metal
    what is "FLEX"? is that the same as BX or MC wires?

  6. #6
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    Quote Originally Posted by hids2000
    what is "FLEX"? is that the same as BX or MC wires?
    Liquidtight Flexible Nonmetallic Conduit (LFNC). A raceway of circular cross section of various types as follows:
    (1) A smooth seamless inner core and cover bonded together and having one or more reinforcement layers between the core and covers, designated as Type LFNC-A
    (2) A smooth inner surface with integral reinforcement within the conduit wall, designated as Type LFNC-B
    (3) A corrugated internal and external surface without integral reinforcement within the conduit wall, designated as LFNC-C
    LFNC is flame resistant and with fittings and is approved for the installation of electrical conductors.


  7. #7

    Default

    Quote Originally Posted by jwelectric
    Liquidtight Flexible Nonmetallic Conduit (LFNC). A raceway of circular cross section of various types as follows:
    (1) A smooth seamless inner core and cover bonded together and having one or more reinforcement layers between the core and covers, designated as Type LFNC-A
    (2) A smooth inner surface with integral reinforcement within the conduit wall, designated as Type LFNC-B
    (3) A corrugated internal and external surface without integral reinforcement within the conduit wall, designated as LFNC-C
    LFNC is flame resistant and with fittings and is approved for the installation of electrical conductors.

    Thanks! I hope home depot or lowes got them for sale. the min order qty online is little too much

  8. #8
    Electrical Contractor jbfan74's Avatar
    Join Date
    Jun 2007
    Location
    Newnan, GA
    Posts
    129

    Default

    Both of them sell a flex kit, which includes the wire, flex, and both connectors.
    It contains 3#10 thhn/thwn wires.
    Yes I am A Pirate-Jimmy Buffett