    Default Outlets on Opposite Sides of Wall/Partition

    Not sure where I saw something about a code requirement that outlets serving rooms on opposite sides of a wall/partition need to be at least 24 inches apart. Intent was to prevent fire spreading across partition thru the penetrations.

    Can anyone give me the specifics of this?

    I have a situation where there is an outlet on an inside wall and I want to mount an outlet on the opposite side of the wall anchoring to the other side of the same stud.

  2. #2
    Licensed Electrical Contractor Speedy Petey's Avatar
    Join Date
    Jun 2007
    Location
    NY State, USA
    Posts
    975

    Default

    I have never heard of such a rule. Not even a local one.

    It is definitely not an NEC requirement.

  3. #3
    Electrical Contractor/Instructor jwelectric's Avatar
    Join Date
    Jun 2007
    Location
    North Carolina
    Posts
    2,523

    Default

    This is a building code requirement and ONLY applies to fire rated walls.

    Allied makes a two hour fire rated box and there is also different methods that can be used to install boxes in a fire rated wall.

  4. #4
    In the Trades brownizs's Avatar
    Join Date
    Feb 2006
    Location
    Springfield, IL
    Posts
    196

    Default

    Also for sound deading purposes, so that sound will not transmit to the room on the opposite side of the wall.