Results 1 to 15 of 21
Thread: AC Blown Fuses at outdoor disconnect
Hybrid View
    Default AC Blown Fuses at outdoor disconnect
    Hello all,
    I have my AC comp. with an outdoor disconnect (picture attached), and the darned fuses keep blowing. Have had problems on and off for a few years, every few weeks or months it would blow. They are the time delay FNR-20 fuses meant for motor protection. Well, today I've gone through about 8 fuses, it blows every 30 minutes or so. Only the replacements go, so I am thinking that I probably have a bad batch of fuses. I even changed locations with the one that hasn't gone, and still, the replacement goes, not the old tried and true that has been in there working fine for about a year. I think it has something to do with dirty power here in the house, the fuse often goes after a slight light flicker. Flippo construction is a couple blocks away working on undergrounding of electrical lines, so my guess is that it is sorta Flippo's fault. So I am wondering, can I replace this outdoor device with a breaker type enclosure? Also, the box states 30 Amp, but I have two 20Amp fuses in it, this doesn't see right. Shouldn't I have two 15 Amp, or am I mistaken and should have two 30 Amp? The Comp.'s CB size at the main panel is 40 Amp. Thanks for the advice.
    Jun 2007
    North Carolina
    On the side of the AC unit will be a name plate that has Minimum Circuit Ampacity xx amps and Maximum Fuse Size xx amps. The xx will be a number.
    If the unit calls for a 20 amp fuse and the 20 amp fuses are blowing it is time to call a AC technician.
    That fused disconnect is designed for a MAXIMUM of 30A, but if your A/C unit specifies a smaller fuse, you can use it. You just can't use a bigger fuse than either the compressor unit specifies, or the box is rated for. For 240vac, you need each side to have the same size fuse.
    If that doesn't fix it, your compressor may be shot...happened to me last year. replaced the whole unit since a compressor was nearly as much.
    Under really heavy power consumption times, like now when parts of the country are in a heat wave, they lower the voltage some (brown out). This will cause the compressor to have to work harder and draw more current. You might check your voltage going to the compressor.
    Jim, thanks for the note. Actually, I do notice it happening more frequently during hot times, figured as much what you said but you have helped to confirm it. I will check the voltage at the comp to see.
    I also think that the company doing the work is causing mini brown outs all around town. I blew fuse after fuse this morning and afternoon, and I know they all stop work promptly at 4:00. Since I replaced the last fuse (same group of fuses that were blowing too) I haven't had a problem, and that is the hottest part of the day.
    I've been trying to put off buying a new unit for at least another year (said the same thing last year too ) so I may need to suck it up. I just ran a new lineset over the winter to accomodate a larger unit, as well as a larger condensate drain from the attic, so I guess I am as ready as ever.
    I'm just worried I will miss the sound of a helicopter taking off or a group of Harleys rolling into town when my AC starts. The thing is about 20 years old I believe, a Sears unit. I can't remember the SEER off hand, but lord knows the thing is not efficient.
    Thanks again to both of you for the input.
    Here is a quick shot of the plate from the side of the compressor. It looks like no matter what a 20 Amp is under sized. Am I correct or just badly misreading things? Should I up it to 30 since the disconnect will support it?
    Jun 2007
    North Carolina
    Quote Originally Posted by santanaf
    Yes indeed
    20A fuses are definitely underrated, the slowblow must have been saving you. But I question why there were 20A fuses in the disconnect? Can you see what gauge the wire is?
    The minimum fuse size is 26.9 and you are surprised that you are blowing 20 amp fuses???? Hello, you need to install 30 amp fuses now. If you continue to have nuisance tripping with the 30 amp fuses, you can increase up to 45 amps, with a new fuse box. Do you need a new compressor? Depends on how energy conscious you are. There may be other stuff that will save you more money per capital outlay.
    DIY Junior Member Maniac's Avatar
    Sep 2009
    Sacramento, CA
    Default Same problem.
    I have a similar situation. AC/Heat on the roof. Fuses blow after a couple of hours. Have been replacing fuses with FRN-R-40. But since the original post I see that the min. circuit amps 49.0 and max fuse amps 60.0. Could the reason the fuses are blowing is because they are below rated at 45 amps?
    The electrician at the local hardware store recommends FRN-R-60 amp fuses.
    What do you all think?
    SAM
    Homeowner Thatguy's Avatar
    Aug 2008
    MD
    Default load test
    Check that the fuse connections are tight.
    Check your 240v supply: Measure the voltage at an unused elec. dryer outlet and turn on an elec. wall oven or all burners of an elec. cooktop.
    If the voltage rises more than 0.4vac when you turn off the load you have a bad connection at, or upstream of the panel.
    Given the age of your house you might want to check the neutral connection and some outlets; for this you need a 120v 10A load [toaster or hair dryer] and the DVM from above. For more accuracy you also should know if you have #12 or #14 wire, aluminum or copper.
    I'd also get a clamp-on ammeter and check the unit's current draw.
    The "trip curve" of the fuse has to match the unit's current draw.
    On average, for a 20 yr old HVAC unit you have a 50% chance of reaching 35 YO.
    Sep 2009
    Sacramento, CA
    Looks like the 60 amp fuses are holding. I'm in Sacramento, CA so now is not a good time to be shopping for a new AC, what with it being 100+.
    I will probably replace it in the fall. The AC tech also said that our returns were too small and that contributes to an overload.
    Sam
    Important factors for your application are:
    1) The wires feeding the condensing unit should be no smaller than 10awg copper.
    2) The fuses should be no larger than 45A.
    3) The Breaker feeding the circuit should be a 40 or 45A HACR type.
    Changing to 60A fuses would be a incorrect and a safety problem.
    http://www.inspectpa.com/forum/forum.php
    My answers are based mostly on the ICC codes. Advice given is my personal opinion and every person performing work should acquire a permit from his/her jurisdiction and get the work inspected. My opinions are not directions to follow for DIYs or professionals
    Sep 2009
    Sacramento, CA
    Default Huh?
    Guess I'm confused.
    The minimum circuit amps. is 49.0 and the max fuse amps is 60.0
    The margin seems to be 'tween the 2. Where would 60 amps be a safety issue?
    The AC is working fine now and hasn't blown anymore. So it seems to me that the solution has been found. Am I missing something?