  1. #1
    DIY Member Montalvo's Avatar
    Join Date
    Feb 2005
    Location
    California
    Posts
    77

    Default Best hot water solution for radiant floor plus domestic hot water?

    I have a 100 gallon commercial water heater (A.O. Smith) in my home that serves my radiant floor heating system (7,100 sq. ft.) plus hot water for two guest bedrooms and our kitchen. The water heater is now leaking (after only five years but, of course, out of warranty) and the radiant heating system installer has recommended against my replacing it in kind. He's suggested instead that I get either a 75 gallon water heater or a tankless water heater for the DHW and that I get either a high-efficiency boiler or a 75 gallon water heater for the radiant system. Now I'm trying to decide how to make the best decision based on economics.

    My average annual gas bill is about $2,700 and it looks like about $1,700 of that is for the radiant heating expense, leaving $1,000 spent on DHW. The radiant guy says I'll be able to install everything but the boiler with fairly nominal costs for re-plumbing but that the boiler will require a PVC stack and, while the chase that currently encloses the water heater's stack could probably accommodate it, the piping would have to go up through through two floors and the attic and that would add to the cost.

    And one last complication...I have an electric pump that circulates the hot water in the pipes to eliminate the long wait for DHW. Can that system work with a tankless hot water heater?

    Based on this, can you help me decide:

    a) tankless or hot water heater for DHW?
    b) hot water heater or high-efficiency boiler for the radiant system?

    I plan to stay in the house for another 20 years (if I live that long!).

    Thanks for any advice you can offer.

    Bob

  2. #2
    Master Plumber master plumber mark's Avatar
    Join Date
    Feb 2005
    Location
    indianapolis indiana - land of the free, home of the brave....
    Posts
    4,243
    Blog Entries
    1

    Talking go with the boiler

    Personally, I would Go with the boiler,
    I doubt that the tankless
    would actually last 20 years..

    the tankless will give you fits with the return
    recirulaiotn line run..

    and I would gamble that the tried and true boiler is
    about the same price or less than a compairable tankless..


    I am wondering
    why not just another 100 gallon commercial heater
    what is the reason for not doing that???????


    2 75 gallon gas heaters is an ok idea too but you will probably
    be wearing out the heater that heats the floor every 5 ;years or so.......
    Last edited by master plumber mark; 06-18-2007 at 01:42 PM.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Go with a high efficiency boiler. Use it to heat an indirect water tank. You won't need as big of a tank since the recovery rate is much higher. The boiler efficiencies on boilers these days are near 95%. Unless you had an electric WH, your efficiency for that is unlikely much better than 70-80%, so you'll save because you can use a smaller tank, and get better efficiency. WIth the HE condensing boilers, they can exhaust up, but generally exhaust horizontally out. The indirect is usually set up as a priority zone. If you get a boiler with a modulating boiler and an outside reset control, it adjusts the boiler temperature for the conditions, some throttling down to as little as 10% of max output. This keeps the cycles down and the lower the temp, the higher the efficiency, approaching a theoretical 98% or so. Most of these HE boilers only run when there is a call for heat, so they don't sit with hot water in them all the time, which on the older ones meant a lot of waste in the summer. On mine, you can set it to allow a bigger excursion from the set point, so it doesn't cycle as much during the summer. On an indirect tank, the better ones have a loss of as small as 1/4-degree per hour, so standby losses are quite small - it may not need to run the boiler for many hours unless lots of water is used during the day. Once people get their showers done in the morning, it may not need to run until evening.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Licensed Grump GrumpyPlumber's Avatar
    Join Date
    Jun 2007
    Location
    Licensed Grump
    Posts
    1,404

    Default

    Hi Jim, let me start by saying hi...from what appears to me to be a very close neighbor.
    My license is in a state just below us, currently getting ready to apply for this state.
    Ironically I'm right at the tail end of installing a Buderus wall mount and couldn't help replying to this thread.
    Some things to know about the condensing boilers....they state AFUE's of well in excess of 90% (up to 98%), but thats at a running temp of 130 degree's...ideal for radiant floors but little else.
    The Buderus I'm installing loses approx. 1.25% efficiency per ten degree's above the 130 mark, so even though it would be approximately 90-92% efficient to run regular baseboard & an indirect it's still worthwhile.
    What irritates me about this is that they don't openly state this ...in fact it was their tech dept that told me over the phone as I was calling with some questions about installation.
    The price of the boiler alone is approximately twice what you pay for a draft vented counter-part...making a difference of about $16-$1800 more.
    The gas co (at least in the state I'm licensed) offers a rebate of $800...after doing the math it actually pays itself back within 5 years, depending on square footage of the house - WITH the rebate.
    One more factor in pricing boilers...Buderus allows for PVC exhaust venting, whereas others require you buy expensive stainless venting.

  5. #5
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Mine seems to run at 120-140 except when firing for the indirect - it feeds radiant. When in this mode it seems like the condensate is a torrent coming down the pipe - it really does suck most of the heat out of the exhaust. We'll see how it holds up, but it does look pretty robust.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  6. #6

    Default

    have you looked into a combi unit like a Baxi Luna?

  7. #7
    Licensed Grump GrumpyPlumber's Avatar
    Join Date
    Jun 2007
    Location
    Licensed Grump
    Posts
    1,404

    Default

    I just took a peak, briefly, at Baxi...they seem to be the same basic thing - condensing, wall mounted.
    One thing about Buderus is it comes with a lifetime warranty (limited of course...but specifically good coverage on the exchanger).

  8. #8
    DIY Member Montalvo's Avatar
    Join Date
    Feb 2005
    Location
    California
    Posts
    77

    Default Thanks for responding...

    Mark, my radiant installer said that he's found poor reliability with commercial installations in residential applications (mine is failing at 5 years) and that's why he recommended going with two separate units for DHW and radiant. And he was proposing tankless as an option only for the DHW, not the radiant. Are you suggesting that the radiant application may have been the reason my water heater failed at 5 years?

    Jadnashua, are you suggesting that I get a boiler for supplying BOTH radiant and DHW? That's something that my radiant guy hadn't suggested and I'm curious about how it would work. Does the "indirect water tank" supply both the radiant and the DHW? Is it a standing tank of heated water, much like a water heater? And what's a "priority zone"? Also, how does the outside reset control work and is that only for the radiant? And if I keep my DHW circulation pump running all day (currently, it comes on for 15 minutes each hour), wouldn't that require that the boiler would need to cycle more frequently than twice a day? Sorry for all the questions but as you can see, I'm clearly no plumber!

    GrumpyPlumber, if I use a horizontal exhaust on the Buderus, does it have to have a minimum upward slope or can it be truly horizontal?

    PoorPlumr, I haven't looked at any brands yet but I'll check out Baxi Luna. Is it a boiler?

    And in case it matters, I live in the Sacramento area with winter lows typically in the high twenties. The water heater is in a large equipment room off the garage and the longest run for DHW is about 70'.

    Thanks again, folks!

    Bob

  9. #9
    Licensed Grump GrumpyPlumber's Avatar
    Join Date
    Jun 2007
    Location
    Licensed Grump
    Posts
    1,404

    Default

    Montalvo...if your plumber is working with radiant tied into a water heater and hasn't mentioned boiler options...I dunno 'bout that.

    A water heater is intended primarily for potable use... 5 years sounds good for what it's being put through (constant firing in the winter months to keep up).
    IF...and only IF you, for some reason, decide to stick with the water heater...ask your plumber what an "anode" is - he'll explain.
    AO Smith generally comes with a 6 year warranty, but I don't think it's intended for use as a "boiler".
    Do some math...a water heater runs at 60-65% efficiency...with a lifetime of 5 years for your useage and a cost to replace of anywhere from at least $1100 to $1,400 or more for a 100 gal - depending on type.
    Even a low end draft type boiler runs at 80-82%...and many offer a 20 year warranty.
    For roughly $2,000 more you can get a condensing boiler...they run at 90-95% and you can run both radiant and indirect hot water off them.
    Condensing boilers come with even better warranties.
    Take your average gas bill and figure it out...figure in the average cost per year for replacement as well as gas cost

    The vent on a condensing boiler is suggested to slope at 1/4" /foot and needs a sanitary drain to tie into.

  10. #10
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,405

    Default

    Basically, an indirect WH looks like a normal tank. Instead of electric or gas to heat it, it has what amounts to a big coil in it - a radiator. The boiler runs to make the WH tank hot. Since making hot water for a shower is usually more important that momentary heat for the house, it shuts the pump off for the house heat while it is needed to make water for say a shower. Since the boiler is tyically much larger heat source than that used to heat a normal tank, you get faster recovery and can usually end up with a smaller tank. You can get them with stainless steel tanks and a lifetime warranty...you should essentially never have to replace the tank.

    You'd run the radiant heat with a separate pump, and use a mixing valve to keep the water temp for the radiant low enough so that when the boiler runs hotter, say to heat the WH, it won't overload the radiant circuits which normally are only in the 110-130 degree range, depending on design.

    An outside reset control is used by the boiler control to adjust the heating curve of the boiler...if it senses it is only 40 degrees outside, it won't make the water as hot as it would if it sensed it at 0-degrees. By making the boiler adjust to the outside temperature, it runs longer and at the lowest temperature it can. The intelligent boilers will also monitor the return water temperature and adjust the level as well. This is the most efficient mode. Ideally, the boiler basically runs. On and off wears it out and after it gets everything hot, if it isn't needed anymore, you've got a whole bunch of hot water heating up the boiler room rather than the house.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  11. #11
    DIY Member Montalvo's Avatar
    Join Date
    Feb 2005
    Location
    California
    Posts
    77

    Default OK, let me see if I've got this right...

    GrumpyPlumbr, first let me explain that my radiant installer did suggest getting a boiler as an alternative, although only for the radiant system (relying on a WH or tankless WH for DHW). My system is gas so I assume that any discussion of an anode doesn't apply; is that right? And you mentioned the need for a "sanitary drain" in conjunction with a boiler's exhaust. Since my equipment room is above grade but below the level of my sewer system, I assume that I'd have to somehow connect the boiler's exhaust to the sump pump that pumps from the sink in that room up to the sewer line. Is that right?

    And Jim D, it sounds like you're recommending that I get a boiler with a) an indirect tank for DHW and b) a separate pump with a mixing valve for the radiant system. But from your description, it doesn't sound like an outside reset valve would make sense in my climate. With mid-to-high 20 degree temperatures being the lowest we get and with a need to reduce the boiler output with a mixing valve on the radiant system, I assume that I could permanently set the boiler to the lowest setting to ensure a minimum amount of on-off conditions. If I did that, how would it effect the efficiency? And can you explain how I'd figure the sizing on the boiler and the indirect tank? I assume I have to start by figuring the maximum demand for both the radiant system and the DHW. But then what?

    Maybe I'm trying to figure out too much of this on my own and should just call in some vendors to get their proposals. But I get nervous when I rely on folks intent on making money at my expense. And I've been living with a system that, although professionally installed, probably wasn't optimally designed to begin with.

    Thanks, guys.

    Bob