Thread: what is a vacuum relief valve for?

  1. #1
    DIY Member northman's Avatar
    Join Date
    May 2007
    Location
    Washington
    Posts
    31

    Default what is a vacuum relief valve for?

    on a water heater/expansion tank installation?

    Looking at the Watts site to size an expansion tank, they show a vacuum relief valve installed at the water heater. What is the purpose? Is it necessary or are they just trying to sell parts?


    Greg

  2. #2
    Customer Service Manager Plumbing Wholesale Peanut9199's Avatar
    Join Date
    Apr 2007
    Location
    Ontario, Canada
    Posts
    876

    Default

    "Vacuum Relief Valves are used in water heater/tank applications to automatically allow air to enter into the piping system to prevent vacuum conditions that could siphon the water from the system and damage water heater/tank equipment." and no you don't need it.

  3. #3
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    My city requires them on new installs along with a tempering valve. My guess is to prevent what may be heated water that has sat for awhile in the water heater from being sucked back into the rest of the potable water. Since all of the water is supposed to be potable, not sure why, but as I said, it is code in my city.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default vacuum vent

    If the heater is in an upper floor level or attic, then the negative pressure created by a broken pipe draining the heater could collapse the walls of the heater. In this case, the installation requires a vacuum vent to relieve the negative pressure. It is not required if the heater is in a basement or first floor because those installations cannot create high negative pressures.

  5. #5
    Master Plumber Dunbar Plumbing's Avatar
    Join Date
    Apr 2005
    Location
    Northern Kentucky/Greater Cincinnati Area
    Posts
    2,943

    Default

    Required on most commercial applications regarding restaurants, nail shops, beauty salons, where chemicals/cross connections are possible above mild.
    Read what the end of this sentence means.

  6. #6
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,605

    Default valve

    Those applications do not require a vacuum relief valve, they require backflow prevention devices, and the higher the possible contamination level, the more sophisiticated the device has to be.