Kitchen Sink Venting

Users who are viewing this thread

Massillonmarine

New Member
Messages
8
Reaction score
0
Points
0
Location
Massillon, OH
I bought my house from an auction. This is my first home and I'm only somewhat handy. A guy I went to school with offered to do all my work. Long story short, he quit halfway through. My kitchen sink had no drainage issues whatsoever before he installed the new sink (deeper tubs) and garbage disposal. My sink has drainage issues. It fills up on one side and eventually the other and then they both rise together. He exclaims that all I need to do is wire the disposal and run it....that it would fix all my problems. Well, I wired the disposal and ran it (with water, without water, turning it on and off to create some air movement in the water) and nothing worked. It used to take an hour or so to drain, now it's taking hours to drain. I don't know if all I need is an under-sink vent or there is something wrong with the existing vent (IF THERE IS EVEN ONE!) I don't know cause like I said, I bought this at auction. I could not get any info on the house from the auctioneer, title company, or the city. Posted below is a pic, sorry it's not more well lit. My camera made it too bright with flash and not enough without. Anyway....have at it...I would appreciate some help.

C340282.jpg
 

Kordts

In the Trades
Messages
547
Reaction score
1
Points
0
Location
exurban Chicago
Number 1: get rid of the trap on the right. I would install a cleanout and rod it out. It might need a vent also.
 

Massillonmarine

New Member
Messages
8
Reaction score
0
Points
0
Location
Massillon, OH
Maybe I should have stated this in my original post. Could all help be broken down into Barney-style answers. I'm not hip with the plumbers lingo. :D I do know what a trap is though.
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
trap

The trap you do not need is the upside down "P" shaped thing next to the disposer. That by itself will not cause your problem. You probably have a plugged drain somewhere in the building, not necessarily the sink drain, given your piping arrangement, which is preventing the drainage. A plumber should be able to determine where the problem is and correct it.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
massillonmarine said:
My kitchen sink had no drainage issues whatsoever before he installed the new sink (deeper tubs) and garbage disposal. My sink has drainage issues. It fills up on one side and eventually the other and then they both rise together.

Like has been said, there is nothing in that sink's plumbing that would cause that kind of problem. One side of the sink fills the other simply because the water in neither has any place to go, and that means the drain line is clogged somewhere. With the sink temporarily disconnected, you might be able to use the pressure from a garden hose to blow down into that drain line and dislodge the clog.

Also, the water supply lines there both look to me like regular PVC, and if so, that is a problem since CPVC should have been used.
 

Yersmay

Writing, constructionDIY Member
Messages
61
Reaction score
0
Points
0
Location
Los Angeles
I'm by no means a pro but I'm posting because I'm curious. Isn't this a good example of an 'S' trap? And isn't that against the rules? If there is no vent to this set up, wouldn't that in itself explain the drainage problem?
 

Massillonmarine

New Member
Messages
8
Reaction score
0
Points
0
Location
Massillon, OH
leejosepho said:
Also, the water supply lines there both look to me like regular PVC, and if so, that is a problem since CPVC should have been used.

It is PVC, this is what it says on the it.......3/4" Silver-Line PVC-1120 SCH. 40 PR.480 PSI @ 73degrees F ASTM D-1785 (NSF-pw)] 2B SL-M NC 01/17/07

We went through a ton of leaking/bursting pipes because he bought the wrong glue. Eventually we got the right glue, but he didn't cure the glue long enough which lead to more leaking/bursting pipes. I paid a lot of money to keep redoing these. Currently I have a a super small bubble up leak that has been pretty steady for over a month in the same spot. I'm just waiting until it pops apart so I can re glue it instead of be having to redo it (it's right at a "t" and would be a lot of work to redo). I do have alot of pressure issues with this. I think I have some air in the line, but I'm not sure how to get it out. I have the water shutoff to the tub upstairs cause it just leaks water right out of the tub faucet if I don't. The toilet and sink have water though. I'm so hard up on money that I am trying to avoid a plumber. My old landlord is supposed to come over and do my work for cheap, but he's so busy with his new truck driving job.

Anywho.....one project at a time. I want to get this sink taken care of, then I'll move on to the water issues. I think I am going to take the drain apart and flush it and possibly get a snake for it. Thanks for the advice, keep it coming. Also, if any of you have the ability to draw on my pic that would be nice. I've seen it done on other posts. What would you use to make this change to the downward P trap?
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
massillonmarine said:
... if any of you have the ability to draw on my pic that would be nice. I've seen it done on other posts. What would you use to make this change to the downward P trap?

I do not know the issue with the "S" trap, if that is what this is, but I cannot imagine this not working properly:
 

Attachments

  • C340282.jpg
    C340282.jpg
    16.8 KB · Views: 960

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
Your drain issues are nothing compaired to the problems you could face with a ruptured water line. I would suggest you turn off the water every time you leave the house until it is fixed.
 

Geniescience

Homeowner
Messages
2,137
Reaction score
4
Points
0
Location
humid summers hot, humid winters cold
yes it is an S trap. Problems do arise with S traps: they cannot guarantee to hold the seal against sewer gases. The fact that professional plumbers haven't commented on it yet doesn't mean it is an OK installation. The first really big problem was the other P trap, in series with this S trap.

Some recent threads here have dealt with inserting an AAV and a small stub of pipe to make it into a P trap; please note that although AAV's solve that one big problem with S traps but they (AAV's) are not bulletproof themselves, for a few reasons.

david
 

Geniescience

Homeowner
Messages
2,137
Reaction score
4
Points
0
Location
humid summers hot, humid winters cold
no, sorry. I'm at the limit of my knowledge and i don't want to risk adding more words than may be accurate. I've never had to deal with S traps in my experience, and whatever I could say would essentially be hearsay rehashed and reworded, or internet based learning reworded. I wouldn't want to pollute this thread with posts that say very little. The thread originator may need to know that it's an S trap, and what to do about, so it could be relevant to add more information about it, so don't think I'm against adding information here. Search in this site and elsewhere on the internet and let us know what you learn too. There must be an easy way to explain it to your satisfaction and everyone's. :)

david
 

Kordts

In the Trades
Messages
547
Reaction score
1
Points
0
Location
exurban Chicago
S-traps aren't vented. That's why they are illegal. They siphon out too easily. Drains that are double trapped also drain slow. You only need one trap, but it should be vented. After that is done, any other drainage issues can be addressed.
 

Markts30

Commercial Plumber
Messages
625
Reaction score
1
Points
0
Location
Phoenix, AZ
Take the vertical drain pipe coming from the floor and extend it then glue on a wye for a cleanout and above that a san-t... Above the san tee put an AAV (ie a Studor-Vent)...
From the san-t branch, pipe to one PTrap and then use a continuous waste kit to tie the sink and disposer into one line....
 

Massillonmarine

New Member
Messages
8
Reaction score
0
Points
0
Location
Massillon, OH
markts30 said:
Take the vertical drain pipe coming from the floor and extend it then glue on a wye for a cleanout and above that a san-t... Above the san tee put an AAV (ie a Studor-Vent)...
From the san-t branch, pipe to one PTrap and then use a continuous waste kit to tie the sink and disposer into one line....


Funny that you said that while I was gone at the store. I pretty much surmised on my own that I needed that based on other threads and pics of other installs. I'll let you all know how that goes and I'll post an updated pic when it's all done. I guess I have to wait 24 hrs for the All-purpose pvc glue to cure, right?
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
massillonmarine said:
I guess I have to wait 24 hrs for the All-purpose pvc glue to cure, right?

Yes, but I believe my can also says something about being able to use the plumbing in 30 minutes or so. I usually wait an hour or two before pressurizing supply lines, but I only stop everyone in the house from using drains during my actual assembly ... and I have never had anything leak.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
kordts said:
S-traps [are illegal because they] aren't vented [and that can cause them to] siphon out too easily.

I re-arranged your words only because that is how my mind works, Kordts, and if the above still says what you said, I now understand. The "S" can slow the flow, but the "S" also means the line is not going horizontally into a vented line, correct?

I think I got it, David!
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
This is an ideal situation for a P trap, san T and AAV. Then this will work right.

After that work on the water lines.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,533
Reaction score
354
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
cpvc....and hot water ... question....

actually, you could leave that whole drain line alone
under the sink if you so wished.... , it
isnt right and it isnt pretty....but it will work,,,,
-----------------------------------------------------------------

like everyone already said you go big troubles in
your water lines.....big troubles.....


you really are not supposed to use that white cpve plastic
on anything but COLD water lines.....or so I am told....


They dont even want you to use cpvc on the relief valves
comming off the water heaters either....claim it cant handle the heat...

. I dont see a problem off the t+p valve myself...its only a non pressurized drain...
----------------------------------------------------------------------

but my question about cpvc.....

I dont think the problem is in the actual pipe....

The problem with it is at the glued joints???
They cannot with stand the constant heat and presure....??

Or is the problem at the connections to things like
shown under this sink...

.hot line male adapter to the
brass conncetion....does it snap off in the threads???

what has everyone seen im their travels through
this plumbing wonderland???
 

Massillonmarine

New Member
Messages
8
Reaction score
0
Points
0
Location
Massillon, OH
leejosepho said:
I do not know the issue with the "S" trap, if that is what this is, but I cannot imagine this not working properly:



I really haven't been around my house to do much, but I did fix this horizontal tube thing. It didn't help. I'm not sure if I should do the work to install the undersink vent or if I should just call a plumber.

C340361.jpg


Let's not get side-tracked by the water line thing. One step at a time. Do you think I should run drain cleaner into the drain first before I attempt to do any undersink venting? Every pipe pictured is completely clear, I should know, I took the entire thing apart.
 
Last edited:
Top