Drum trap or not?

Users who are viewing this thread

Rick.a

New Member
Messages
84
Reaction score
0
Points
0
Location
Palmer, Massachusetts
As part of a total kitchen remodel I need to reinstall a kitchen sink drain. The existing 1 1/2 pvc goes straight down thru the floor to the crawlspace. The prior setup had a drum trap. I was told that this was because of the long drop from the sink. Should I put in another drum ( I have heard negative references to them) or use a P-trap? If I use a P-trap followed by an ell to go straight down it will then be an S which is not good. Is this correct? So what should I do?

The vent is also a problem since I cannot go up. I want to use an AAV to solve this.
 

Terry

The Plumbing Wizard
Staff member
Messages
29,942
Reaction score
3,459
Points
113
Location
Bothell, Washington
Website
terrylove.com
I would use a p-trap with AAV if you can't find a vent going up.

https://ipscorp.com/plumbing/brands/studor/

sink_rough_island_b.jpg


Here is part of an island vent.
 
Last edited:

Peanut9199

Customer Service Manager Plumbing Wholesale
Messages
869
Reaction score
2
Points
0
Location
Ontario, Canada
A p/trap with an elbow is fine (s/trap) drum traps are good to catch straws or popsicle sticks that fall down a kitchen sink, but a union p/trap works just as well.
 

Markts30

Commercial Plumber
Messages
625
Reaction score
1
Points
0
Location
Phoenix, AZ
Peanut9199 said:
A p/trap with an elbow is fine (s/trap) drum traps are good to catch straws or popsicle sticks that fall down a kitchen sink, but a union p/trap works just as well.

I would have to disagree and go with what Terry said...
PTrap into a santee with a "studor vent" style AAV above it...
STraps are illegal/not code compliant and tend to cause problems....
 

Dubldare

Plumber/Gasfitter
Messages
284
Reaction score
1
Points
0
Location
MN/ND
Being this is a "total kitchen remodel", why can't the budget be found to bring your plumbing up to standards that have been around for over 125 years?

Why can you not go up? Six inches above the flood rim of the fixture allows you to route horizontally to where you can go up. 45 degree offsets are considered vertical runs below the tops of fixtures. Relocating the waste line going through the floor and 'dirty' arming back toward your fixture's trap is a good way to clear windows that may be above the sink. Another option is an island vent, yet this still requires an accessible vent, which may be in an interior wall.

I usually look at it as this, if it is structurally impossible to provide venting for a fixture at a given location, consider an island vent or a different location. If there's a bit of wallboard in the way, it can be patched. If it's too much work to do it correctly, consider not having the fixture alltogether.
 
Last edited:

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,538
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Dubldare.... overkilling a project....

Their is doing things the right way and then their is makeing a mountain out of a mole hill.

this is not the space shuttle or a hospital, its a kitchen sink drain.---in a kitchen

So why in the world would you want to find a way to make an island vent for something that would work fine for the next 50 years with a Auto air vent and p trap????

They make those Auto Air vents and have been useing them for at least 25 years.....they are legal almost everywhere...because they work great.....

so why would you want to beat your braines out trying to
tear up a wall and install an isalnd vent and do something
that way...

especially when that drum trap did an ok job

for 100 years already??
 

Dubldare

Plumber/Gasfitter
Messages
284
Reaction score
1
Points
0
Location
MN/ND
Mark, with all due respect, I'm going to re-iterate my stance.


master plumber mark said:
Their is doing things the right way and then their is makeing a mountain out of a mole hill.

Since when is correctly venting a fixture during a "total kitchen remodel" making a mountain out of a mole hill? Since when are non-vented fixtures the "right way"? Since when is the "let sleeping dogs lie" mentality ok because it's too much like work to do it right; or to even let the asker consider what is approved from a code perspective v/s 'what you got has worked'.


this is not the space shuttle or a hospital, its a kitchen sink drain.---in a kitchen

Does not matter from a code perspective. Fixture is a fixture no matter where it is.


So why in the world would you want to find a way to make an island vent for something that would work fine for the next 50 years with a Auto air vent and p trap????

The island vent is listed by me as a code approved alternative to conventional venting methods. This brings me into your next statement:

They make those Auto Air vents and have been useing them for at least 25 years.....they are legal almost everywhere...because they work great.....

You imply that something that's been around for at least 25 years is going to become something that will last 50 years. AAV's have been used for over 25 years in trailer houses, per the very relaxed HUD and DOT codes which govern such dwellings.

Now I don't beat my drum, but I too am a master plumber in both Minnesota and North Dakota. Minnesota has a proprietary plumbing code which predates the UPC (1933), and North Dakota has an amended 2000 UPC. Neither code allows for AAV's.
Minnesota will allow an island vent (boston loop or as seen here: https://terrylove.com/images/island_vent.gif ) if structural limitations prevent conventional venting methods. North Dakota will allow the boston loop, or the more common method of increasing the fixture branch sizing twice to 3", and venting the 3" within 15' of the fixture.


so why would you want to beat your braines out trying to
tear up a wall and install an isalnd vent and do something
that way...

especially when that drum trap did an ok job

for 100 years already??

Because I know better.

One thing that the AAV does not account for is backpressure. The AAV can only prevent backsiphonage, it cannot relieve the drain of any positive pressure that may exist due to upsteam fixtures discharging, downstream blockages or foaming from nearby suds producing fixtures. Additionally, up north where it gets cold, we are required to ventilate the city's sanitary sewer system through our DWV systems. Come on up here next time it's cold, I'll take you on a roof of any vacant building you choose. We can bask in the warm air that's coming up through the VTR's. :D





Perhaps the biggest issue as to why I find myself typing this, (rather than doing stuff that I might get benefit from) is we, as professional plumbers, have an obligation to provide information that is codeworthy. Now, some may say that's overkill, but codes are nothing more than minimum standards. Doing something to code is not overkill, it is the bare minimum of what is needed to be found sufficient. We do have an obligation not only to our craft, but to the end user, to ensure that they have a system that is safe and requires minimal maintainance.

I, as a professional, shouldn't be in the buisness of circumventing minimum standards and neither should the rest. I treat my responses as if someone were paying me +$100/hr to do their work. I treat myself as a resource of information. If that information goes against the grain somestimes, so it goes. I don't find myself at the doctor asking for only the good news or what I want to hear.

Sorry for the schpiel, had to get that out.
 

Geniescience

Homeowner
Messages
2,137
Reaction score
4
Points
0
Location
humid summers hot, humid winters cold
wow. Can i quote this?

I'll try to make a little summary for the original thread question, and include some background information.

A long distance drop down to a P trap can lead to the P trap being sucked open by the water's own inertia, so it is not recommended.

An S trap, even on a low-flow drain like a little sink, has a permanent problem since it relies on the rest of the plumbing system to compensate for its lack of venting. There is never any guarantee what is, or is not, happening in the rest of the house.

A drum trap has so many problems that it is not acceptable anywhere, AFAIK.

The only bulletproof option is a P trap, and a vent, near the sink.

A few ways to do that (vented P trap) have been described; the easiest way (with an AAV) is far from being bulletproof, for the reasons described eloquently in the previous post.

david
 

Dunbar Plumbing

Master Plumber
Messages
2,920
Reaction score
10
Points
0
Location
Northern Kentucky/Greater Cincinnati Area
Website
www.KoldBreeze.com
To add to dubldare's statement I know without any doubt that KY has some of the strictest codes in regards to plumbing. So when I hear about AAV's and wet vents, loop vents or any other SHORTCUT that is allowed by one state and NEVER by KY's standards....I look at the necessity and function theory behind the logic.

I got a friend in Michigan that they allow AAV's for everything. You'll see a new addition wiht small vent covers throughout the home with them being used as access to those AAV's.

Now folks, the majority of homeowners don't fix their plumbing until it fails. Remember that AAV's are a mechanical device: it will fail. Either the diaphragm ripples and loses it seal or the spring weakens/tempers/breaks just like in a backflow assembly from repeated use.

AAV's are a shortcut. They'll fail and the non-knowing homeowner will then be subjected to sewer gases which can cause health problems, create bacteria enriched atmosphere.

I really wish all states followed the strict standards that KY and NY follow. Such a better design and creates a better operating system with less failure. I've heard of 2" or 1.5" stacks going through the roofs, no cleanouts at the base of stacks, no isolation valves on toilets and kitchen sink faucets or lav's ....??!?

I personally like my state having a difficult code.
 

Master Plumber Mark

Sensitivity trainer and plumber of mens souls
Messages
5,538
Reaction score
357
Points
83
Location
indianapolis indiana - land of the free, home of
Website
www.weilhammerplumbing.com
Codes are diffferent everywhere

I completely understand what you are talking about..

dont take me personally......

codes are different everywhere.....so be it....

Indiana is pretty rlaxed when it comes to plumbing
compaired to all around us...that is true.true ..true...

I really ought to post some of the things I have seen that
is considered code here......

so you can all GAWK and laugh at
the new home plumbing
that is considered ok here....

I have seen stuff done in new homes that actually
made me stop in my tracks and stare for a while...

here in Indiana you can run a kitchen with no vent ,
only a aav under the sink, we can run a 3 inch drain to the kitchen
and then reduce it to 2 inch and simply put a 2 inch elbow tothe trap...

the downside to all this is just about anyone can do plumbing here
and get away with it......


a difficult code keeps real plumbers in business and
makes plumbing more of a trade or a guild. that it used to be.....

but it has to be enforced all the way into the hardware stores....

----------------------------------------------------------------------------------------

you got to do what is code in your state..
and ..I completely understand....



but I would venture to bet you that if you were to go to

LOWES in your home town...
you will find the Auto Air Vents...and the average
do it your selfer will install it before going to the troubles
that the plumber would ....

so their is a fine line between code and economics and

landing the job ......

if you tell someone you have to do this and that to meet
code for $350 more

and they see a 2 dollar auto air vent at LOWES
that they can install themselves......with a can of glue , a hack saw
and a little advice from the dummie at LOWES...


what do think the odds are he might do it himself
and tell you to take a hike....???
 
Last edited: