garcanser said:
Thank you all for your suggestions.
Currently, all my control valves are driven by 24 VAC relays. If I understand the suggestion correctly, I need to use one of the 24 VAC relays to drive the 240 VAC power relay.
I think there may be a bit of confusion about what relays you have, and some standardization of language would be helpful.
A relay is really defined by the coil voltage and the current capacity, so when talking about the Volts of a relay, you should be referring to the coil voltage.
Most relays are rated for 24, 120, and 240 Volts at the contacts, regardless of the coil voltage.
Your computer is producing a logic output of 5 Volts. That 5 Volt signal is apparently driving another relay with a 5 Volt coil. From your comments earlier, you are using 24 Volts through the contacts of that relay to operate the valves.
You should check the Amp and Voltage rating of the relay that you are using to operate the valves. That will determine if you are able to operate a larger relay through those contacts.
It is quite likely that you can use that relay to operate the coil of a larger "Pump" relay. I recently installed a system with a remote control where a very small relay was able to handle 3 Amps at 120 Volts, and that would be plenty.
If you determine that the relay that operates your valves has the Amps/Volts capacity to operate a relay or contactor for the pumps, then you can get inexpensive Double Pole relays to operate the pumps. You only need a Single Pole relay to operate the 120 Volt pump but there is a lot of benefit to having only one model in your inventory.
You should get relays that are "horsepower rated". Enclosed relays that will handle 1/2 HP at 120 Volts or 1 HP at 240 Volts are readily available with 24 VAC or 120 VAC coils. Check stock number 1EZ90 and 1EZ92 at
www.grainger.com
If I need something larger I usually use a 2-pole "Definite Purpose Contactor" by Square D, such as Grainger stock no. 5B124, 5B126, 5B127, 5B129, 5B131, or 5B132.