Thread: Vent size

  1. #1

    Default Vent size

    I am installing a new 3" pvc line for a toilet, the vent will be 3' downstream. My ? is will 1.5" pvc be ok for vent size?
    Last edited by damorej; 02-10-2005 at 12:32 PM.

  2. #2
    Plumber RioHyde's Avatar
    Join Date
    Sep 2004
    Location
    Cincinnati, Ohio
    Posts
    339

    Default

    That really depends on the code requirements for your part of the country. Here, the vent must be a minimum of half the size of the drain it serves so 1-1/2" vent would be the minimum size for a 3" drain. However, in reading through the posts since I've joined, I've seen that some municipalities require a 2" vent for a toilet. Call your local building dept. and ask what the requirements for your area are. I'm sure they'll be happy to help you out.

    On a side note, I'm installing a bathroom in my basement at the present time. My vent for my toilet will be "oversized" to 2". I just like to "overdo" now and then especially on my own plumbing.