Help with vent design.

Users who are viewing this thread

dcf1999

Member
Messages
49
Reaction score
0
Points
6
Location
Illinois
I'm remodeling my bathroom. The main problem I have is that all my fixtures (toilet, sink, and shower) will exceed the maximum distance from trap to vent; therefore, I have to install new vents. Let’s take the toilet for example. Its 12' from the soil stack/vent. I was going to run a tee off the fixture arm, extend a vent vertical about 5 or 6 inches, then using an elbow run it horizontal about 1.5 feet to the base of the wall. I would then run the vent vertical through the wall and into the attic where I'd run it horizontal to the main vent. Is this acceptable?
 

Jimbo

Plumber
Messages
8,918
Reaction score
18
Points
0
Location
San Diego, CA
vents cannot run horizontal until they are 42" above the floor level of that bathroom.
 

Markts30

Commercial Plumber
Messages
625
Reaction score
1
Points
0
Location
Phoenix, AZ
Actually I do believe vents can have graded horizontal runs below flood rim level )below floor, slab etc...), but they should be avoided if possible and when done, drainage fittings must be used...
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
1 town I work in will not allow anything but straight up to above the flood rim or 42" which ever is higher B 4 you can angle at all.

And absolutely no flat venting of any kind anywhere I have worked.
 

dcf1999

Member
Messages
49
Reaction score
0
Points
6
Location
Illinois
Now I'm really stuck!

I had my bathroom all planed out but this plumbing thing is a nightmare! My toilet is going to be 12 feet from the main soil stack/vent, therefore I need a vent. I'm running 3" piping from the flange to the stack. If I can't run a vent off the fixture arm as I mentioned above, does anyone have any ideas how I can run a vent? I'm having a similar problem venting my shower drain but if I can learn how to vent this toilet, I’m sure I can used the same concept for the shower which is 15 feet from the stack. Thank you for all your help so far! I really appreciate it!
 

Markts30

Commercial Plumber
Messages
625
Reaction score
1
Points
0
Location
Phoenix, AZ
Sketch us a quick floor plan...
There is probably a solution to your problem...
As well, tell us where you live...
Codes do differ from place to place...
 

dcf1999

Member
Messages
49
Reaction score
0
Points
6
Location
Illinois
Here you go

Here is a rough drawing (Don't have CAD at work :) ) I hope I attached the picture correctly. If you need any more information please ask as I need all the help I can get. Thank you again! The soil stand/vent in the picture is actually just the vent. The toilet sites right on top of the soil stack and the vent branches off the stack with a "y" fitting. It's an older house with all cast iron. I'm probably going to rip out the cast iron from the ground up and make it all PVC. Also the picture showes the new closet flange offset from the soil/stack, but it's directly inline. I don't think that matters but I though I'd add it anyways.
 

Attachments

  • floorplan.jpg
    floorplan.jpg
    20.8 KB · Views: 441
Last edited:

Frenchie

Jack of all trades
Messages
1,239
Reaction score
0
Points
36
Location
Brooklyn, NY and Fire Island, NY
You can still T into the arm, I think

Please explain better about the stack. Your toilet's going to be capping the stack? No arm at all?

There's another vent 12' away?

What?
 

dcf1999

Member
Messages
49
Reaction score
0
Points
6
Location
Illinois
Currently the toilet is above the stack and there is a vent that comes off the stack to the roof. I'm moving the toilet 12 or so feet away from the stack and am going to conect to the stack with 3" pipe. I just need to know how to vent that 12' long fixture arm going from the toilet to the stack.
 