Thread: Water Heater as source for Baseboard Heat

Hybrid View

  1. #1

    Default Water Heater as source for Baseboard Heat

    I'm hoping you guys can help me get a handle on this...


    We bought our house about two years ago. Main heat souce is gas furnace hot air, but house has an addition (family room 16'x16' and bathroom 7'x6') that used a hot water heater with a circulator pump to provide heat to baseboards (22' of baseboard in family room and 5' of baseboard in the bathroom).

    The first winter the water heater/baseboard system did a good job of heating the room, but I don't think it was very efficient (high gas bills). We wanted to upgrade the system as the water heater was old (probably 20 yrs or so) because I was afraid of tank failure (it had a lot of rust), but money was tight, so we just turned it off and used an electric oil-filled radiator to heat the space in the begining of this season.

    When we could afford it last month, I had a heating contractor come out and give me a recommendation. He told me even the smallest boiler would be too big for my application and told me the best bet would be to just swap the water heater for a new one. ( The old heater was a 30 gallon 40k btu unit) He recommended a 40 gallon 40kbtu unit. I asked if there would be a difference in the max water temp between the old and new units and was told no.

    Three weeks ago they put the new unit in and replaced my old thermostat for the room with a new programmable unit.

    Here's the rub...

    Even with the water heater set at high, the room won't get as warm as it did with the old heater. ( I even insulated the lines (36 ft total) that run through the unheated crawl space under the room with no increase in heat output. They were un-insulated with the old heater with no problems.

    They came out today and checked the whole system and basically said it was fine and as good as I can expect.


    My question is, did the old heater have a higher temp output?

    I asked the guys if they new what temp the new heater would produce and they said they were unsure but it was probably around 130f and that was plenty.

    When I asked if a unit that put out higher temp water woul help my situation, I was told no, that my baseboard would still only put out the same amount of heat no matter how hot the water flowing through the pipes was..something about the fins being heat-saturated. Which I find hard to believe.

    After they left I did some reasearch...

    Bradford White says the max temp for a residential heater is 160f and my old heater was probaly rated at 180f. They said their combination unit with the heat exchanger and their commercial units both do 180f (My heating contractor told me that both the combi and the commercial units would be the same max as my residential unit)

    Did I get hosed?

    Is the heater insufficient for my heating needs?

    Any thoughts?


    Sorry about the length of this post, but I really need to figure out what to do.


    Thanks,
    Steve

  2. #2
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    The difference in temperature between the room and the water determines how much heat you can distribute along with the velocity of the water (i.e., the changeover). If you check the specs on the baseboard heaters, they will have values like x BTU/foot at 180-degree input. It will probably also be spec'ed at different input temps, and will also indicate the gallons/minute of flow. Measure the water temp - if you don't have a gauge, it wouldn't be a bad idea to put in two, one on the output and one on the return.

    There could be a restriction somewhere (a valve not fully open maybe or a check valve stuck) that is preventing proper flow. Did they change the circulator?

    If you search around on the net, you can locate a heat load calculator (spreadsheet, typically) that will tell you how much heat you really need to keep that area warm. If you have enough heat capacity in the heater, but can't get the rooms warm, then you may not be flowing it fast enough. There is a limit on how fast you can flow the water before you risk cavitation and wear on things. It is also possible that there is an air lock, and things just aren't circulating. Are there any air extraction devices in teh system? Did they purge the system properly? Is the pump the right size?
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  3. #3

    Default

    Jim,

    Thanks for your reply.

    I'm out of luck on the specs for the baseboard (installed in 1972 and long gone).

    No temp guages, but they measured the temp of the output and return today (output 126f return 124f, although he wrote 126.5 and 121.5 on my paperwork).

    As far as restrictions go; new valves and fingers crossed.

    same ciculator pump (3 speed) now set on 3 to see if it makes a difference.

    It's a closed loop, but I have had to add water 3 times since the install when the pressure has dropped to "0". Could this be air being purged from the air extraction valve? I heard a lot of gurgling in the baseboard prior to the last pressure drop.

    They said they bled the system after the install.

    Pump info: Grundfos type UPS 20-42, 40w outp, Class F,
    3: 2620 rpm winp 95
    2: 2300 rpm winp 70
    1: 1800 rpm winp 50

    Thanks again for your help.

    Steve

  4. #4
    Retired Defense Industry Engineer jadnashua's Avatar
    Join Date
    Sep 2004
    Location
    New England
    Posts
    21,382

    Default

    Since it is a closed system, when you have to add water, there must be a leak. If it leaks and you let the heater get too low on water, you will ruin it. For a boiler, there is usually an automatic water makeup valve with a backflow preventer. Nominally, you should have the water pressure at about 15 pounds or so and have both an air extraction device and an expansion tank.

    SInce the return water was essentially the same temp as the supply, the water isn't circulating. My guess is that you would see maybe as much as a 50-degree difference between input and output (or more) on a cold day. I feed my in-floor heat around 130-degree water, and it returns at around 60-70-degrees on a cold day.

    The pump should be taking water out of the hot side of the WH, and returning it to the cold side.

    The system sounds like it is air locked and the pump can't push the water through the radiators.

    A WH isn't really designed for this, but can work - you will wear it out quicker.

    If you do the heat loss calculation you would know how much heat you need. Some of the boilers today are modulating - they can adjust their output down from their maximum level. The smaller ones generally available can go down to maybe 15K BTU. This type of boiler costs more to buy and install, though, than an older design.
    Jim DeBruycker
    Important note - I'm not a pro
    Retired Defense Industry Engineer; Schluter 2.5-day Workshop Completed 2013, 2014

  5. #5

    Default

    Jim,

    Thanks for the reply.

    I've checked the whole system for water leaks and have found nothing.

    My old water heater set up had a feeder valve that the contractor said I didn't need since it is a closed loop (he hooked up the new heater without the feeder in the loop).

    I've been running 20 psi and have an air extraction device and an expansion tank.

    I had the same thought about the water not circulating because of an air lock and asked the contractor about it...he said the pump would "push" the air through in that case and it would go out the valve. Is theis untrue?

    Here's a couple of pics of my set up:











    any additional thoughts?

    thanks again,

    Steve

  6. #6
    DIY scratch-pad engineer leejosepho's Avatar
    Join Date
    Nov 2006
    Location
    200 miles south of Little Rock
    Posts
    2,474

    Default

    Quote Originally Posted by eastcoaststeve
    I had the same thought about the water not circulating because of an air lock and asked the contractor about it...he said the pump would "push" the air through in that case and it would go out the valve. Is this untrue?
    I know nothing about your kind of heating system, but I know the heaters in the back of my old school bus have air bleeders for a reason, and that reason is that the water pump cannot push the air through the heater cores at the ends of long runs of 1" hose. I would say you have an air lock somewhere.