Slope in pvc drains

Users who are viewing this thread

Ehlinn

New Member
Messages
26
Reaction score
1
Points
0
Location
Maryland
I have a general question about the maintaining the slope in pvc drains. I am running a length of "horizontal" drain to a vertical line and I will be making the connection with a T. But the t comes off the vertical at 90 degrees. How do I slope the horizontal run of pipe going from my drain to the T? Do I just force it to have the 1/4 inch per foot slope? Sorry if this is a little unclear, it is awkward to explain. I just don't want any leaks. Thanks for any help.

Eric
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
Slope in PVC drain

You won't have to actually "force" the PVC to make the 1/4"/ft slope. PVC is flexible enough to conform to the trench.
 

hj

Master Plumber
Messages
33,603
Reaction score
1,042
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
tee

If you were using threaded pipe and fittings, the tee would be tapped so that the "pitch" is automatic. PVC and ABS fittings have enough flexibility that you can put the proper pitch, and a lot more if necessary, without affecting the integrity of the joint.
 
Top
Hey, wait a minute.

This is awkward, but...

It looks like you're using an ad blocker. We get it, but (1) terrylove.com can't live without ads, and (2) ad blockers can cause issues with videos and comments. If you'd like to support the site, please allow ads.

If any particular ad is your REASON for blocking ads, please let us know. We might be able to do something about it. Thanks.
I've Disabled AdBlock    No Thanks