.5 psi is too high for the units unless the control valves also have regulators to reduce it to about 4-5 inches water column, which is about .2 psi. Either the burner coming on is creating a surge which blows the pilot out, which could be the most likely problem, or the regulator is causing a momentary drop that puts the pilot out. A second regulator for one of the two devices should cure the problem.