Water heater drain pan

Users who are viewing this thread

Xenomorph

New Member
Messages
41
Reaction score
0
Points
0
I am just wondering what you guys do to connect the vertical tailpiece/downspout to the galvanized water heater drain pan. The tailpiece is brass, but the pan is galvanized. Is it possible to solder the 2 together using acid flux and regular solder?

thx.
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
The T&P is 3/4 threaded brass that will accept a copper male adp. with soldered pipe going to a upright T with a 3" X 1.5" coupling bushed reduced down to 1" into the T. It needs a 2" air gap between 3" PVC and the copper. This is what is required where I am. They don't want the T&P going into the pan incase the T&P leaks the heater would be sitting in water.
 

Plumb or Die

Plumbing Instructor
Messages
38
Reaction score
0
Points
0
Location
Southern BC Canada
Yes, you can

Yes you can solder it, just heat slowly to not overheat and blacken the galvanized pan. A always solder them, a buddy of mine silicones his.
 