The T&P is 3/4 threaded brass that will accept a copper male adp. with soldered pipe going to a upright T with a 3" X 1.5" coupling bushed reduced down to 1" into the T. It needs a 2" air gap between 3" PVC and the copper. This is what is required where I am. They don't want the T&P going into the pan incase the T&P leaks the heater would be sitting in water.