Thread: Pressur Test Bathroom DWV System

  1. #1

    Default Pressur Test Bathroom DWV System

    I'm putting 5lbs of pressure on the system. How long should it hold? After about 5 minutes it goes to about 4.5 lbs. Can anyone advise me?

    Thanks,

    Brian

  2. #2

    Default

    It is possible that the initial loss of pressure is due to cooling of the air...if you are pressurizing with air. To get much of a pressure test.. I'd put at least 10-15 psi... wait a few minutes (maybe 5) then check pressure then check again in 15 minutes to see if it lost any pressure. I'm thinking that it should hold steady for 15 minutes... If pipes are accessible and exposed you can paint or spray on soapy water at joints and plugs.... good sudsing dishwashing liquid works great.

  3. #3
    Commercial Plumber markts30's Avatar
    Join Date
    Sep 2006
    Location
    Phoenix, AZ
    Posts
    630

    Default

    In Phoenix, standard the city looks for is either 10' of water head or 5lbs pressure for 15 minutes with no pressure loss...
    Re-pressurize it and spray the joints with soapy water (dish soap and water works well). Any bubbles will indicate a leak... You can then fix it...

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,673

    Default leaks

    Kid's "Mr. Bubble" or similar works better because it will stick to the joint longer. Sometimes you can come back 5 minutes later and see a ball of foam at the leaking joint.