air, no water

Users who are viewing this thread

steve cutter

New Member
Messages
3
Reaction score
0
Points
0
I have an in-basement one pipe shallow well pump that stopped pumping yesterday. The pump runs and the guage as it enters the exp. tank goes up to about 18-20 psi but just produces air. I have a hose bib valve/hose where the pump disch. line enters the tank and when I run the pump with the hose submerged it just bubbles. If I open the valve fully the pressure goes to zero, if I just crack it it holds pressure but no water. I've ruled out the pump and suspect a leak in the suction line. I replaced the foot valve in the well about 3 weeks ago because I heard the pump running in the night and figured it was either that or a leak. The last couple of days there was air in the lines in the morning and the pump was "growly" buut it pumped up and shut off. I've tried priming but nothing. Another thought was a stuck foot valve, but where is the air coming from?
Appreciate any help. Don't really want to dig up the line but that's my best guess at this time
 

Cass

Plumber
Messages
5,947
Reaction score
7
Points
0
Location
Ohio
You could have a leak in the line but it would lose pressure after pumping up. Do you know how many feet of water is in the well above the footer valve.
 

Speedbump

Active Member
Messages
4,511
Reaction score
12
Points
38
Location
Riverview, Fl.
How far down to the water from the pump?

Since this happened after you made repairs and the problem is different than the last one, I would check what you did. Look for air leaks, which have no taste or odor and can't be seen either. The suction line is where the air would come from. Anywhere from where the pipe screws into the front of the pump to the footvalve.

bob...
 

Gary Slusser

That's all folks!
Messages
6,921
Reaction score
22
Points
38
Location
Wherever I park the motorhome.
Website
www.qualitywaterassociates.com
And since this happened when you were using water, you may be pulling the water level down to the foot valve inlet, sucking air. Known as a dry well condition.

When you primed it, did hold water for say 5 minutes without you having to add more water? If not you have a leak and the foot valve is a prime suspect.

Why did you replace the old foot valve?
 