tviapiano
New Member
Hi there. I have read some great postings here and I have learned a lot from everyone's questions and answers.
My mother-in-law has a WM oil-fired boiler, forced hot water and tankless domestic hot water. About a year ago, she started hearing banging coming from the heating system sometimes. Her hot water at the taps is always way too hot. I was at her house once when it happened and I went down to the boiler room. The temp/pressure gage on the boiler read over 200 deg. F! I assume the banging was from the water boiling in the system.. The Honeywell L8124C aquastat HI set point is set to about 150 deg F.
She called her heating guy, and he increased the pressure in the system.... Huh? What about the aquastat NOT breaking at the proper temp? I told her to ask him that and he dismissed that as nonsense.
A few months later, the problem was still happening, so she called him back. He changed the fill valve/regulator, check valve, etc. saying that the noise was coming from there... Again, not even acknowledging the HI set point issue.
I was at her house yesterday and the same thing: banging! I went into the boiler room and the temp was over 200 deg F and the pressure was at about 0! I flipped the manual lever on the fill valve a little, and it clicked and the boiler started to fill and the pressure went up to about 15 psi, just I believe it is supposed to be...
So, obviously the fill valve may need replacing since it seemed to have stuck closed. But, does it sound like the aquastat may need replacing? I assume there is no way the aquastat could be operating properly if it does not break at the HI set point, right?
Thank you all for any advice you can provide.
My mother-in-law has a WM oil-fired boiler, forced hot water and tankless domestic hot water. About a year ago, she started hearing banging coming from the heating system sometimes. Her hot water at the taps is always way too hot. I was at her house once when it happened and I went down to the boiler room. The temp/pressure gage on the boiler read over 200 deg. F! I assume the banging was from the water boiling in the system.. The Honeywell L8124C aquastat HI set point is set to about 150 deg F.
She called her heating guy, and he increased the pressure in the system.... Huh? What about the aquastat NOT breaking at the proper temp? I told her to ask him that and he dismissed that as nonsense.
A few months later, the problem was still happening, so she called him back. He changed the fill valve/regulator, check valve, etc. saying that the noise was coming from there... Again, not even acknowledging the HI set point issue.
I was at her house yesterday and the same thing: banging! I went into the boiler room and the temp was over 200 deg F and the pressure was at about 0! I flipped the manual lever on the fill valve a little, and it clicked and the boiler started to fill and the pressure went up to about 15 psi, just I believe it is supposed to be...
So, obviously the fill valve may need replacing since it seemed to have stuck closed. But, does it sound like the aquastat may need replacing? I assume there is no way the aquastat could be operating properly if it does not break at the HI set point, right?
Thank you all for any advice you can provide.