    Default 1/2" PEX supply lines to Moen Shower valve

    Hey,
    I am trying to rough in my basement bath, and I have used PEX piping for the entire job. I am trying to install my shower valve, and was curious on what the correct way to connect PEX piping to shower valve?
    I purchased a Moen Shower Valve with interior threads, do i attach the PEX directly to the hot and cold water holes with an adapter or do I attach a few inches of copper and then attach the PEX to the copper pipes sticking out of the valve?
    Same with the connection from the valve to the shower head? Do i have to sweat the copper pipes and attach it to the shower head? or can I just go PEX from the valve to the shower head.
    Both the shower head and valves have female threaded holes.

    Thanks for the help in advance.

  2. #2
    Plumber Cass's Avatar
    Join Date
    Nov 2005
    Location
    Ohio
    Posts
    5,984

    Default

    If the position is right for the shower wall and the valve can be secured well to the framing you can run the PEX to the valve. Personally I like to secure the valve and run copper to the framing and secure it then run my PEX from there. Both will work.
    Last edited by Cass; 12-31-2006 at 04:13 AM.

  3. #3

    Default

    The Sioux Chief "Shower Up" kit is really good for this.Includes everything you need.Not all places have them however.


    http://www.siouxchief.com/Supply/Kits/Shower-Up-Kits
    Last edited by Terry; 12-11-2012 at 04:37 PM.

  4. #4
    Moderator & Master Plumber hj's Avatar
    Join Date
    Aug 2004
    Location
    Cave Creek, Arizona
    Posts
    25,632

    Default shower

    Since this is a shower, you can get away with using PEX for the shower riser. If it were a tub/shower doing so would create several problems.

  5. #5
    DIY Junior Member jeffResistor's Avatar
    Join Date
    Jan 2009
    Location
    Washington DC
    Posts
    6

    Default

    Quote Originally Posted by spooner View Post
    Hey,
    I am trying to rough in my basement bath, and I have used PEX piping for the entire job. I am trying to install my shower valve, and was curious on what the correct way to connect PEX piping to shower valve?
    I purchased a Moen Shower Valve with interior threads, do i attach the PEX directly to the hot and cold water holes with an adapter or do I attach a few inches of copper and then attach the PEX to the copper pipes sticking out of the valve?
    Same with the connection from the valve to the shower head? Do i have to sweat the copper pipes and attach it to the shower head? or can I just go PEX from the valve to the shower head.
    Both the shower head and valves have female threaded holes.

    Thanks for the help in advance.
    I realize I'm 2 years late on this, but I just connected a Moen shower valve yesterday with 1/2 in pex, and maybe I can help others who run across this thread. For the shower valve I used 1/2" PEX males adapters for the hot and cold in, as well as the out to the shower head. For the shower head I used a 1/2" PEX drop ear elbow.

    Since both the shower valve and the drop ear elbow connect directly to the framing with screws, there's no need to rely on copper to hold them in place. I used exterior screws to guarantee against rust and corrosion. Also, since all of the adapters are direct to PEX, you don't have to sweat copper stubs for your connections, which would create extra potential points of failure. The PEX lines are then secured to the framing with the normal 1/2 inch plastic talons, although once everything was connected it was pretty solid and I doubt the talons were necessary.

    I'll repost when I get a minute to snap a photo.
    Last edited by Terry; 12-11-2012 at 04:40 PM.

  6. #6
    Master Plumber Dunbar Plumbing's Avatar
    Join Date
    Apr 2005
    Location
    Northern Kentucky/Greater Cincinnati Area
    Posts
    2,943

    Default

    Good luck with that jeff.



    There's a class action lawsuit on those fittings breaking off/snapping under stress. They still sell them but that doesn't mean they are good.


    Take a look at how thin that brass is in the barbed area of that fitting; that's why they are breaking over time and they made these thin to accommodate the ability to work without creating reduced flow by reducing the inside dimension of the piping.

    The industry has now brought a serious reduction in flow to the fixture by having these fittings all dropping the size of the pipe before it reaches the fixture. This causes the problem with flow reduction when numerous fixtures are in operation in a home.


    you don't have to sweat copper stubs for your connections, which would create extra potential points of failure
    Care to explain this statement?


    1/2" copper delivers exactly what its dimensions state, 1/2" water flow.


    Keep an eye out for your brass fittings in your wall; when they snap it is instant, without warning, in your sleep, while on vacation, away at work, water running till the dog floats out of the basement and the pool table sits in the driveway.


    http://www.zurnclassaction.com





    I bet you're thinking Awe G'Dammit! I found a way to get from soldering and the **** I bought at Lowe's is junk! Sufferin' succatash!
    Last edited by Dunbar Plumbing; 01-04-2009 at 08:47 AM.
    Read what the end of this sentence means.

  7. #7
    DIY Junior Member jeffResistor's Avatar
    Join Date
    Jan 2009
    Location
    Washington DC
    Posts
    6

    Default

    Quote Originally Posted by RUGGED View Post
    Care to explain this statement?
    The original post was asking if he had to sweat copper stubs to attach to the shower valve in order to make the connection to PEX possible. That would mean two sweated copper joints per each connection in addition to the pex connection (one for the copper male adapter and one for the copper to pex adapter). Going directly to pex reduces the number of connections (by 8 in my system), which are all potential points of failure.

    Thanks for the heads up on the fittings. Now that I've spent the last year converting 1/2 of my house to pex with the vanguard manibloc system, I guess it's back to the drawing board, or propane torch...

  8. #8
    DIY Junior Member jeffResistor's Avatar
    Join Date
    Jan 2009
    Location
    Washington DC
    Posts
    6

    Default Photos of PEX shower installation

    Here are a couple of photos showing the shower valve and head connections I described above.

    The shower valve:
    dead link

    The shower head elbow (note: the red pex coming out of the elbow is just for testing and keeping debris out while the concrete board and tile go up):
    dead link

    The overall installation:
    dead link
    Last edited by Terry; 12-11-2012 at 04:42 PM.

  9. #9
    Master Plumber Dunbar Plumbing's Avatar
    Join Date
    Apr 2005
    Location
    Northern Kentucky/Greater Cincinnati Area
    Posts
    2,943

    Default

    DUDE,



    You've got that PEX strained into the hot/cold ports of that valve. Those 2 connections you linked are going to be the first 2 to snap off with the way you have that "pulled" to make that turn up vertical.



    Those tube talons?


    They're plastic, with the exception of the nail itself.


    In about 3/4/5 years with the constant temperature changes in those water lines from hot to cold, cold to hot, back and forth, cool down to room temperature,

    those tube talons get very brittle and snap right where the hook end goes back to the nail. I've seen it more times than I care to say.

    This will take time before they break but you'll know this years from now when they snap and valve now moves freely in the wall.


    I got no reason to lie, I'm telling you how it goes in plumbing with those materials.


    And I don't even want to start with my chirade on that Moen faucet. If you don't pull that cartridge and grease it every 2 years in that assembly it'll take a dump truck, special tools to get it out of that valve body.


    THAT is when you'll see those tube talons snap.
    Read what the end of this sentence means.

  10. #10
    DIY Junior Member jeffResistor's Avatar
    Join Date
    Jan 2009
    Location
    Washington DC
    Posts
    6

    Default

    Quote Originally Posted by RUGGED View Post
    You've got that PEX strained into the hot/cold ports of that valve. Those 2 connections you linked are going to be the first 2 to snap off with the way you have that "pulled" to make that turn up vertical.
    Thanks for all of the warnings! I'm kind of too far into the pex conversion to turn back, so I guess I'll have to wait and see what nightmares are in store for me in the next few years. I suppose I'll be leaving a $h1tl0ad of access panels everywhere I have a connection! And I'll be popping them open every day to have a look...

    On the valve connection, should I use the 90 degree bend guides to make the connection more straight on, or is it the same risk regardless? Thanks again!

  11. #11
    DIY Junior Member jeffResistor's Avatar
    Join Date
    Jan 2009
    Location
    Washington DC
    Posts
    6

    Default Bronze fittings?

    Hmmm, looks like on that class action web site, one of the companies switched to the Viega bronze fittings after hundreds of failures of the brass Zurn fittings. Any experience with Viega bronze? Now's the time for me to switch them out before the walls get closed in.

  12. #12

    Default Class Action Suit

    I've been reading about the class action lawsuit that you're talking about too. I'm in the process of going through a bath remodel and I used PEX for everything so obviously I wanted to make sure the pipes would stand the test of time. I'm in the Washington, DC area and every PEX supply house that I talked to told me they've never had any problems with PEX (including Zurn PEX). They indicated that it has a lot to do with the area of the country that it's used in, the water, etc. Honestly, I don't know what to believe, but I thought I'd throw that out there as some food for thought.

  13. #13
    Software Engineer BlackNoir's Avatar
    Join Date
    Mar 2009
    Location
    Centerville, MN
    Posts
    17

    Default

    I'm curious, couldn't you just put in a couple 90 degree PEX elbows instead of that sharp bend? Is there any reason not to use PEX elbows? Seems like it would be the same as using copper. Especially if you used rigid PEX pipe instead of the flexible stuff.



    I'm going to be doing a shower soon and am planning on doing it with PEX and this was pretty much the route I was planning on going.

    -BlackNoir

  14. #14
    Plunger/TurdPuncher kingsotall's Avatar
    Join Date
    Aug 2008
    Location
    Flagstaff, AZ Sitting on an upside down 5 gallon bucket next to the GO 68HD
    Posts
    1,260

    Default

    Those aren't "Pex" elbows. Those are sharkbites. See if your locale approves of those type of fittings in concealed locations.

  15. #15
    Software Engineer BlackNoir's Avatar
    Join Date
    Mar 2009
    Location
    Centerville, MN
    Posts
    17

    Default

    True, they're not actually PEX elbows.. I guess I was just using them as example. The question still stands, which is, is there any reason not to use PEX elbows?

    But, a good point about the sharkbites in concealed locations. I might just have to invest in a crimper after all.

    So if you shouldn't use sharkbites and the Zurn Brass connectors have a class action lawsuit against them making me NOT want to use them, how exactly can you use PEX in a concealed location? Would you recommend the new Zurn Platic connectors? I saw a bunch of those at ******* but hadn't heard anything about them yet.

Similar Threads

  1. supply lines for new shower
    By RobertZ in forum Shower & bathtub Forum & Blog
    Replies: 4
    Last Post: 03-26-2012, 10:26 PM
  2. Help with a shower supply lines install
    By Dom Z in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 11
    Last Post: 08-18-2009, 10:18 AM
  3. Solder supply lines to valve or use threaded?
    By johngaul in forum Shower & bathtub Forum & Blog
    Replies: 1
    Last Post: 11-14-2007, 06:46 AM
  4. moen shower valve supply question
    By spooner in forum Shower & bathtub Forum & Blog
    Replies: 3
    Last Post: 02-18-2007, 04:42 PM
  5. Can I use flexible supply lines from shuttoffs to shower valve?
    By Jhawk in forum Plumbing Forum, Professional & DIY Advice, Tips & Tricks
    Replies: 16
    Last Post: 10-10-2006, 06:24 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •