Basement floor drain - vent required?

Users who are viewing this thread

mao

New Member
Messages
4
Reaction score
0
Points
0
Excellent forum! And thank you in advance for any insights.

I am making plans to add a bathroom to my first floor by utilizing a floor drain in the basement. The current drain, 3-inch, is trapped but not vented, and is approximately 15 feet from the main stack in the house. I intend to remove the trap, install a 3-inch PVC going up-stairs to feed the new bathroom, which will be vented, etc from there. I would like to install a new floor drain in the basement, tying into the 3 inch line using a wye. Question: does the floor drain need to be vented? I’m thinking: yes, or the rush of water in the 3-inch line from the bathroom upstairs would siphon out the floor drain trap. But I’m also thinking no: that a 3-inch line is large enough so this won’t happen. If it is vented, what would be general practice: to use an AAV or to have a vent head up through the floor into the bathroom, where it would tie into the bathroom vents and ultimately go through the roof. That would mean another hole in the floor, not impossible, but not great either.

Block diagram is attached as a pdf.

Thanks for any info.

Mike
 

Attachments

  • basement_floor_drain_plan.pdf
    6.3 KB · Views: 1,515

Randyj

Master Plumber
Messages
1,060
Reaction score
2
Points
36
Location
Alabama
If I were going to put all that sewage producing stuff above that floor drain I would seriously consider putting a backflow preventer on the floor drain branch. If it should clog downstream of the floor drain then you gonna have a basement floor full of s**t. If possible/practical, add a trap primer to the floor drain. If you want to do it right, add a vent to the fd branch also.
 

Randyj

Master Plumber
Messages
1,060
Reaction score
2
Points
36
Location
Alabama
kordts said:
Even if the trap was vented, you couldn't use it to vent fixtures.
Why is that? Something I'm missing here... and I'll admit, my understanding of venting is questionable.....
 

mao

New Member
Messages
4
Reaction score
0
Points
0
That does not exactly make sense to me as it is written. Assuming I install a vent as described, each fixture would be vented, but all the vents would tie together at various points ultimately passing through the roof as a single vent. The vent from the basement would remain separate from the drains the entire way, but would tie into the vents from the bathroom fixtures some 42 inches or so above the floor in the bathroom. Then that single vent pipe would proceed up through the second story and through the roof.

I am really thinking I require a vent downstairs for the floor drain now, although in reality I do not think it would make a difference if the vent were not there.
 

mao

New Member
Messages
4
Reaction score
0
Points
0
Interesting point on the backflow preventer. I'll have to think about that.
 

Kordts

In the Trades
Messages
547
Reaction score
1
Points
0
Location
exurban Chicago
The vents can all tie in together in the attic, but a you can't just pull a vent of a main for all the fixtures on the main. Each fixture needs it's own vent. We usually try to vent each fixture off the branch before it hits the main, but sometimes you have to take your vent off the main. regardless, each fixture needs a vent. You can't pull 5 or 6 branches off a main, then pull one vent off the main for all of them.
 

camerono

New Member
Messages
3
Reaction score
0
Points
0
One more possibility

If you're getting the floor drain inspected, check with your local inspector. You should be able to wet vent the p-trap to another fixture line.

Also, because basement floor drains tend to be used little, the water in the p-trap can evaporate over time and allow sewer gas to escape into the living space. As a result, some jurisdictions may require you to ensure the trap stays wet by using a trap primer (I've also heard this called a wet trap).

A model I've used a few times is made by pppinc. There are really two parts to it:

attachment.php


- a valve (Model P-2 for single floor drain)
- BAP adapter

Example picture located here: http://www.pppinc.net/common_files/.../Precision_Priming_Adaptor/P-Trap-Diagram.jpg

p_trap_primer_example.jpg
 
Last edited by a moderator:

hj

Master Plumber
Messages
33,602
Reaction score
1,038
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
Tp

That one is installed into a tee in the line and the "drain" from it goes to the floor drain, usually under the floor to prevent a tripping hazard. Other models are installed in the cold water line so the water flows through them.
 