    Please excuse me if this has already been covered 1 million times. I did some searching and could not come up with an "exact" answer to my particular scenario.

    I am adding a 1/2 bath to my home and had some questions on pipe sizes.
    The 1/2 bath is also going to double as a laundry room. I am converting a fairly large "mud room" for this that has a crawlspace under it. The room will contain a toilet, pedastal sink, washer/dryer, and a utility sink. This room is directly on the oposite side of my kitchen sink and dishwasher.

    Now for the questions:

    1. What size supply lines should I be running for all this? I was planning on Teeing off the kitchen supply that is 1/2. Is this acceptable?

    2. What size drain should I use to connect to the main? Is 3in enough? Currently I believe there is a 1 1/2in drain for the kitchen sink/dishwasher that I was going to replace.

    3. What size vent should I use? 2in??

    Thank you in advance for any and all answers.

  2. #2
    Homeowner geniescience's Avatar
    Join Date
    Nov 2005
    Location
    humid summers hot, humid winters cold
    Posts
    2,152

    Default yes, yes, yes [1,2,3]

    yes to all questions. Nothing mission critical here.

    david

  3. #3
    DIY Junior Member KGP's Avatar
    Join Date
    Dec 2006
    Location
    NJ
    Posts
    3

    Default

    Thank you for confirming my answers David!

  4. #4
    Forum Admin, Expert Plumber Terry's Avatar
    Join Date
    Aug 2004
    Location
    Bothell, Washington
    Posts
    14,208
    Blog Entries
    1

    Default

    1/2" pipe is too small for all those fixtures on the water supply.

    http://www.terrylove.com/watersize.htm

    Toilet can go 3", 2" vent
    Kitchen sink should be 2" waste 1.5" trap arm and trap, 1.5" vent
    Washer 2" waste, 2" p-trap, 1.5" vent
    Utility sink, 2" waste, 1.5" trap and arm, 1.5" vent
    Pedestal lav, 1.5" waste, 1.5 trap, 1.5" vent


    Washer and utility sink, with 2" standpipe for the washer
    Hammer arrestors on the water supply.

  5. #5
    DIY Junior Member KGP's Avatar
    Join Date
    Dec 2006
    Location
    NJ
    Posts
    3

    Default

    Thanks Terry. So should I use 3/4?

    How about the drain and vent? Should I still use a 3in drain and 2in vent for all of these considering I put all the traps/drains for each according to the listed sizes? These will all be connecting together to connect to the existing system leaving the house. (this is on the opposite side of the house in the basement)