The 2" vent from the basement washroom can be used for the 1st floor vent if you join the 2" vent to the 1st floor vents at least 6" above the fixture flood rims...
This means that you cannot join the vents together until about 42" above the 1st floor bathroom floor...
If it is just the toilet you need to vent on this 2" pipe, measure from the floor to the rim of the WC and add 6"... That is the lowest you can join into the existing 2" vent.