Type: Posts; User: Mrk3cobra; Keyword(s):

Search: Search took 0.12 seconds.

  1. Replies
    33
    Views
    914

    Problem solved, I pulled the jet and nozzle...

    Problem solved, I pulled the jet and nozzle replaced it with the next size bigger. The pump now cuts out at 52psi and cuts in at 32 psi and with the sprinklers running pressure stays above 30 psi....
  2. Replies
    33
    Views
    914

    But the tank has no water I can move it back and...

    But the tank has no water I can move it back and forth. I will change the jet and nozzle.

    thanks, Pete
  3. Replies
    33
    Views
    914

    The sprinklers are low water use, there is 6...

    The sprinklers are low water use, there is 6 heads per valve each head is .65 GPM. the pressure drops off when the tank is empty.
  4. Replies
    33
    Views
    914

    I tried to add back pressure by slowly closing...

    I tried to add back pressure by slowly closing the ball valve, the pressure did not go up until I had the ball valve 3/4 of the way closed. At that point the pressure went up to 30 PSI but the...
  5. Replies
    33
    Views
    914

    I will try choking back on the ball valve, will...

    I will try choking back on the ball valve, will this help with the volume of water. When I tested the pressure was ok until the pressure tank ran out of water then the pressure dropped instantly to...
  6. Replies
    33
    Views
    914

    2335323354OK I let some air out of the pressure...

    2335323354OK I let some air out of the pressure tank, it is at 28PSI with the tank empty did not help. I let the pump run until 38PSI then I turned on the sprinklers and the pressure slowly droped to...
  7. Replies
    33
    Views
    914

    I will check the tank pressure when I get home...

    I will check the tank pressure when I get home today. I will also run a test with the pump running and the pressure at 40 psi I will turn on the sprinklers and see if the pump can maintain close to...
  8. Replies
    33
    Views
    914

    There is no regulator the two pipes that go down...

    There is no regulator the two pipes that go down the well are connected directly to the pump, which is only 1' from the well casing. Should I install the bigger or smaller nozzle to get more volume,...
  9. Replies
    33
    Views
    914

    the pump has no label on it. The regulator (the...

    the pump has no label on it. The regulator (the part that controls the cut in and cut out)is on the motor, and the gauge is on the pump.It has worked fine for me for the last 15 years.
  10. Replies
    33
    Views
    914

    The deep jet motor says on it 1/2 HP manufactured...

    The deep jet motor says on it 1/2 HP manufactured by GE. This is an old pump maybe 20 years old.
    The new injector I bought came with 3 nozzles I think a 51,52,53 I used the 52 and the venture that...
  11. Replies
    33
    Views
    914

    I will test today...

    I will test today...
  12. Replies
    33
    Views
    914

    I will try and let some air out of the tank. How...

    I will try and let some air out of the tank. How would too much precharge in the pressure tank cause the symptoms I have. Just trying to understand a little better.

    Thanks, pete
  13. Replies
    33
    Views
    914

    The pressure gauge is on the pump...

    The pressure gauge is on the pump...
  14. Replies
    33
    Views
    914

    The pressure stays at 10 psi until I turn off the...

    The pressure stays at 10 psi until I turn off the sprinklers then it goes up to 50 psi..
  15. Replies
    33
    Views
    914

    Need help troubleshooting low pressure

    I have a deep well jet pump used for irrigation. I just replaced the injector at the bottom of the well because I could not get more then 35 psi. Now the pump shuts off at 50 psi and cuts in at 30...
  16. Replies
    0
    Views
    225

    Help replacing deep well injector

    I just pulled the pipe out if my well to inspect the injector. I have a GE 1/2 HP deep well jet pump. The water level is at 18 feet, the injector and the foot valve are at 25 feet. After doing some...
  17. We're do I buy a new injector online, and how to...

    We're do I buy a new injector online, and how to do I size the injector with my well setup.

    Thanks, pete
  18. Does all the water go through the 1/4" hole in...

    Does all the water go through the 1/4" hole in the center of the funnel? Does some water go around the outside of the funnel?
  19. So if the 1/4" hole is open the injector is good?...

    So if the 1/4" hole is open the injector is good?

    Pete
  20. Ok I pulled the Injector, what I see is a small...

    Ok I pulled the Injector, what I see is a small plastic funnel on the 1 1/4 line. There is a 1/4" hole at the bottom of the funnel. There is sand packed around the plastic funnel. This is the first...
  21. Well pump will not build enough pressure to cut out

    I have a GE deep well jet pump 1/2 HP. With a square D 30/50 cut out switch. The pump use to cut out at 50 psi and now the pump will only produce 43 psi and does not cut out. The well is only 18 feet...